    Gree Multi over cooling



    A friend has just installed a Gree Multi to service two rooms. One of the rooms seems to be working normally while the other room over cools and freezes the indoor coil. No error codes. Any idea what might cause this?



  2. #2
    Join Date
    Feb 2008
    Location
    england
    Posts
    505
    Rep Power
    21

    Re: Gree Multi over cooling

    have you checked the interconnecting wiring is not crossed

  3. #3
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Gree Multi over cooling

    I will definitely check that. Thanks.

  4. #4
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Gree Multi over cooling

    You were right. The wires were crossed. We swapped them back and everything works. Thanks.

  5. #5
    Join Date
    Feb 2008
    Location
    england
    Posts
    505
    Rep Power
    21

    Re: Gree Multi over cooling

    you shod always run each unit independently on first start up this way you will no the piping and wiring are correct