    Howden WRV 255
    For a chiller water application Howden state oil pressure to be 200 kPa over discharge and fault at 100 kPa over discharge. Would there be any detriment to the compressor if the oil pressure was run at 300kPa over discharge?
    Jan 2006
    Norway
    1,044
    4
    31
    Re: Howden WRV 255
    No problem, max gas oil diff as recommended by Howden is 500 kPa.
    (can't share the document where it says)
    -Cheers-
    Tycho
    May 2009
    New Zealand
    141
    15
    Re: Howden WRV 255
    Thanks Tycho, just what I needed to know
    Sep 2009
    Iran
    66
    672
    1
    Re: Howden WRV 255
    hi
    the temperature of oil also viscosity of that effect to that difference
    High temp low difference and
    high viscosity high difference (but should be in manufacture recommended compressor rang )