    Mar 2018
    United Kingdom
    3
    Coping with Varying Evaporating Temperatures on Trans Crit CO2 Systems
    I have a scenario whereby I have multiple evaporators operating on the same CO2 condensing unit with widely varying evaporating temperatures.
    I don't know of anyone that offers an EPR valve suitable for high pressures so wonder how I can control the evaporating temperatures in the highest evaporating systems.
    F&V evaporator is at +2°C with the lowest evap temp fixture at -7°C. I can't have the F&V at -7 because the Delta T to the Room (+8°C) is too wide and could dry product.
    I could separate the F&V evaps onto their own condensing units but I need to keep the number of condensing units to a minimum for economic and space reasons.
    Any help/advice would be very much appreciated.
    11,025
    Re: Coping with Varying Evaporating Temperatures on Trans Crit CO2 Systems
    I'm not an expert on CO² but would a plate heat exchanger providing a secondary cooling fluid circuit for the higher temperature circuit be feasible?
    Feb 2011
    scotland
    451
    Could a ICM valve be used as a EPR? Is it for a pack or a cubo2 type of unit?
    3,357
    As Sean mensions, Danfoss will be able to sort you out.
    http://files.danfoss.com/TechnicalIn...dbook_DILA.pdf
    Aug 2014
    75
    508
    You can use either a combination of a Danfoss ICS valve with a CVP (HP) pressure pilot valve as a simple back pressure control valve , or an ICM valve with an ICAD motor plus an electronic controller such as an EKC 361 with a PT1000 temperature sensor for remote control applications . Did this on many supermarket CO2 systems in the UK