    mitsubishi electric outputs and alarm



    My peoples

    What do i need to do to get an alarm output and remote on/off for a mitsubishi electric: pca-m140ka, i presume i need an interface?


    Mostly found in the southern part of this green and pleasant land.

  2. #2
    Join Date
    Dec 2008
    Location
    UK
    Posts
    568
    Rep Power
    24

    Re: mitsubishi electric outputs and alarm

    You will probably need the PAC-SA88HA 5 wire adapter. Best check with Mitsubishi in case the part number has changed.
    Mobile A/C at its best, see avatar.
    Bedford. Now retired and trying to relax.

  3. #3
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,471
    Rep Power
    41

    Re: mitsubishi electric outputs and alarm

    Thank you Hyper!

    For the remote on/off, is it a pulsed signal ie one pulse on, further pulse off?

    Al
    Mostly found in the southern part of this green and pleasant land.

  4. #4
    Join Date
    Aug 2007
    Location
    Russia
    Posts
    138
    Rep Power
    21

    Re: mitsubishi electric outputs and alarm

    No, it is not a pulse signal. SW1 is for remote control block and SW2 is for ON/OFF
    Attached Images Attached Images
    Last edited by narkom; 23-03-2019 at 09:01 AM.

  5. #5
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,471
    Rep Power
    41

    Re: mitsubishi electric outputs and alarm

    Thanks Narkom, the 5 wire has a different set up though:

    https://www.mitsubishi-les.info/data...C_SA88HA_E.pdf

    Orange and green for fault and red and brown for on off?

    Al
    Mostly found in the southern part of this green and pleasant land.

  6. #6
    Join Date
    Aug 2007
    Location
    Russia
    Posts
    138
    Rep Power
    21

    Re: mitsubishi electric outputs and alarm

    CN51 connector is for Fault status (3-4 contacts) and Operation status (3-5 contacts).The output voltage is 12VDC.
    The red and brown wires are not in use.
    For On/off control you should use CN32 connector as I described above. It is potential free connector.
    Last edited by narkom; 25-03-2019 at 04:39 PM.

  7. #7
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,471
    Rep Power
    41

    Re: mitsubishi electric outputs and alarm

    Thank you Narkom
    Mostly found in the southern part of this green and pleasant land.