    ireland
    1,451
    mitsubishi electric outputs and alarm
    My peoples
    What do i need to do to get an alarm output and remote on/off for a mitsubishi electric: pca-m140ka, i presume i need an interface?
    Dec 2008
    563
    Re: mitsubishi electric outputs and alarm
    You will probably need the PAC-SA88HA 5 wire adapter. Best check with Mitsubishi in case the part number has changed.
    ireland
    1,451
    Thank you Hyper!
    For the remote on/off, is it a pulsed signal ie one pulse on, further pulse off?
    Al
    Aug 2007
    Russia
    139
    22
    No, it is not a pulse signal. SW1 is for remote control block and SW2 is for ON/OFF
    ireland
    1,451
    Thanks Narkom, the 5 wire has a different set up though:
    https://www.mitsubishi-les.info/data...C_SA88HA_E.pdf
    Orange and green for fault and red and brown for on off?
    Al
    Aug 2007
    Russia
    139
    22
    CN51 connector is for Fault status (3-4 contacts) and Operation status (3-5 contacts).The output voltage is 12VDC.
    The red and brown wires are not in use.
    For On/off control you should use CN32 connector as I described above. It is potential free connector.
    ireland
    1,451
    Thank you Narkom