    Rack system



    Hi Friends,

    I have a question. At photo below, Danfoss says for using several compressors together on rack system, One of the way to maintain oil level in compressors is Dynamic piping.
    In this issue, By using gas restrictor P2 will be less than P1. This is clear.

    But just this topic is not clear for me, Danfoss says while we use gas restrictor shown below, 90% of oil (coming in suction line) prefer go to upstream compressor. Then as result of higher P1 instead P2 (P1 > P2) extra oil will go to downstream compressor.

    Why 90% of oil prefers go to upstream compressor ? Just for this reason than P1 is higher than P2 ? Gas restrictor is simple thing, Why it forces oil to go to upstream compressor ?

    Thanks.
    11112.jpg



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Rack system

    Please download this Danfoss document and see pages 15 and 21, they should explain more clearly than I can.

    https://www.google.com/url?sa=t&sour...mGscNtFyqiUxNP
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Rack system

    Quote Originally Posted by A.Mortezania View Post
    Hi Friends,

    I have a question. At photo below, Danfoss says for using several compressors together on rack system, One of the way to maintain oil level in compressors is Dynamic piping.
    In this issue, By using gas restrictor P2 will be less than P1. This is clear.

    But just this topic is not clear for me, Danfoss says while we use gas restrictor shown below, 90% of oil (coming in suction line) prefer go to upstream compressor. Then as result of higher P1 instead P2 (P1 > P2) extra oil will go to downstream compressor.

    Why 90% of oil prefers go to upstream compressor ? Just for this reason than P1 is higher than P2 ? Gas restrictor is simple thing, Why it forces oil to go to upstream compressor ?

    Thanks.
    11112.jpg
    Page 7 in Brian's link explains pressure drop in compressor P1 suction causes oil to migrate.