    Question York millennium star delta transition interruption



    YAES 0525, 2 circuits, 1 comp each, starting contactor (principal and star) during 1 to 2 seconds and stopped. Same on the 2 circuits. Checks CT 50ohms, continuity line HP motor protect goldair, winding comp, contactors coil auxiliary contacts, electronic boards supply 5CC 12CC 24CC visual inspections.
    so 30amp clampmeter during 1second,
    Registred board zero amp, 0%, mssg Star/Delta OFF.
    Help plsIMG_20190228_095843.jpgIMG_20190228_095843.jpg



  2. #2
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,471
    Rep Power
    41

    Re: York millennium star delta transition interruption

    Is the issue happening on the transition to delta?
    Mostly found in the southern part of this green and pleasant land.

  3. #3
    Join Date
    Jul 2010
    Location
    Mauritus
    Age
    62
    Posts
    8
    Rep Power
    0

    Re: York millennium star delta transition interruption

    Thks al, yes the interruption occured just 1.5 second after (principal & star)

  4. #4
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,471
    Rep Power
    41

    Re: York millennium star delta transition interruption

    Is there a chance that the auxillary contacts on the contactors are "bouncing" at change over? We had issues with early versions doing this, a fix was to fit a storage heater contactor to slow the transition, maybe change one set of contactors first in case they have worn the contacts down.
    Mostly found in the southern part of this green and pleasant land.

  5. #5
    Join Date
    Jul 2010
    Location
    Mauritus
    Age
    62
    Posts
    8
    Rep Power
    0

    Re: York millennium star delta transition interruption

    Thks, I return on site this morning and tell you

  6. #6
    Join Date
    Jul 2010
    Location
    Mauritus
    Age
    62
    Posts
    8
    Rep Power
    0

    Re: York millennium star delta transition interruption

    Al
    First Thank you,
    _ one before I've changed motor protector on each compressor
    power supply 220V on, contact M1 M2 was tested alone without wiring, as good continuity ohms, that is to say shut.
    _ now wiring of contact (M1 M2) shunted without action protector module, RUNNING
    also I've one of old Texas Klixon 41AA1600E= running 1 circuit right,
    the other old one out of order
    "The 2 news relay (bought 155$each without transport) I'v received ebay,: seller: Shangai Goldair Electric System Co.,Ltd, ref 41AA1600EE Goldair part 16G08 41A OE 240V 2.5amp contact all sames specifications"
    !!!
    Now, I've to found one available spare, if suggest thks
    Whatever AL, thks your attention