Results 1 to 7 of 7
  1. #1
    Join Date
    Feb 2005
    Location
    New Zealand
    Age
    43
    Posts
    26
    Rep Power
    0

    Tools for measuring flow water flow rates through binder access ports



    Any recommendations on a tool to use for measuring flow rates for water + glycol hydronic systems much appreciated



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Tools for measuring flow water flow rates through binder access ports

    It all depends.

    Do you have commissioning valve stations, orifice plates or simply pressure test points across components with known pressure drops.

    Commissioning valve manufacturers may have dedicated test kits or you may be able to get a test kit that is calibrated for many manufacturers.

    For simple pressure drops you could use a simple water manometer.

    Wrong country I know but just an indicator ...
    https://www.bsria.co.uk/instrument/s...oning-systems/
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Jun 2011
    Location
    Australia
    Age
    44
    Posts
    337
    Rep Power
    21

    Re: Tools for measuring flow water flow rates through binder access ports


  4. #4
    Join Date
    Feb 2008
    Location
    england
    Posts
    505
    Rep Power
    21

    Re: Tools for measuring flow water flow rates through binder access ports

    you can buy ultrasonic flow meters on eBay that clamp to the outside of the pipes

  5. #5
    Join Date
    Feb 2008
    Location
    england
    Posts
    505
    Rep Power
    21

    Re: Tools for measuring flow water flow rates through binder access ports

    comtronic is a good flow meter for binder points

  6. #6
    Join Date
    Feb 2005
    Location
    New Zealand
    Age
    43
    Posts
    26
    Rep Power
    0

    Re: Tools for measuring flow water flow rates through binder access ports

    Thanks for all the great options, have emailed the rental company for the ta scope as they are Ta valves.
    Very interested in comtronic and ultrasonic so will read up on them tonight. Thanks for all your help

  7. #7
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,876
    Rep Power
    28

    Re: Tools for measuring flow water flow rates through binder access ports

    The comdronic is a great meter. It gives the Kvs of most manufacturer commissioning sets, valves, orrifice plates. Nice and quick when on site.
    Some say not as accurate as a water box though.
    The difference between genius and stupidity is that genius has its limits.

    Marc

Posting Permissions