Retrofitting York YCAS screw chillers from R22 to R407c
It's been a while since I posted anything here.
I am about to embark on changing some R22 YCAS chillers to R407c and was wondering if anyone out there has some experience they could share with regards to what problems I can expect to come up against. The local York supplier has told me that we will lose about 5 to 6% capacity but that is not a big problem as the units are already oversized for their duty.
I would appreciate any advice regarding the above project. I have been reading some blogs where people are talking about o-rings require changing etc because they change shape with 407c?????
-
14-02-2019, 07:32 PM #2
- Join Date
- Sep 2009
- Location
- Iran
- Age
- 66
- Posts
- 672
- Blog Entries
- 1
- Rep Power
- 19
Re: Retrofitting York YCAS screw chillers from R22 to R407c
Hi
main thing to change R22 to 407C
is cleaning system ( very good) and putting POE type Oli in compressor .
then after running set superheatLast edited by mbc; 15-02-2019 at 08:08 PM.
-
15-02-2019, 02:43 AM #3
-
20-02-2019, 09:21 AM #4
Re: Retrofitting York YCAS screw chillers from R22 to R407c
Thank you gents. It seems that it shouldn't be too difficult as the systems already have POE oil in the compressors.
-
20-02-2019, 08:17 PM #5
Re: Retrofitting York YCAS screw chillers from R22 to R407c
You can find a procedure here, I'm assuming accurate.
https://www.honeywell-refrigerants.c...07c&download=1