    Two condenser use

    Hi... can we use two shell tube type condenser on single reciprocating compressor? Plz give me inlet and outlet hedders drawing

  2. #2
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: Two condenser use

    hi
    might help you1.jpg
    Attached Images Attached Images

  3. #3
    Join Date
    Jun 2014
    Location
    india
    Age
    30
    Posts
    23
    Rep Power
    0

    Re: Two condenser use

    A drawing series connection other perlal connection witch the best

  4. #4
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: Two condenser use

    Hi

    is it depend's on conection sizes
    if your conection is small do parallel if not and you have enough room to put one of them on top of that do series
    on those have same capacity
    in parallel if one of them got leaks you could used other one for short periods
    Last edited by mbc; 08-02-2019 at 05:19 AM.

  5. #5
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,299
    Rep Power
    31

    Re: Two condenser use

    Hi, manmohan ...

    Quote Originally Posted by manmohan View Post
    Hi... can we use two shell tube type condenser on single reciprocating compressor? Plz give me inlet and outlet hedders drawing

    it is possible ...

    what is the main reason to use two condensers ... just curious ;-)

    ... in general it is better to connect condensers in parallel ...


    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  6. #6
    Join Date
    Jan 2002
    Location
    Canada
    Posts
    35
    Rep Power
    0

    Re: Two condenser use

    Hi Mammohan
    Some tips, If you design
    In serie, just take for account that the pressures losses through each condenser as to be added. Which increase the head pressure, and then decrease the overall efficiency. The second condenser might run often flooded if you have load fluctuation. Insure that the first condenser is located at a higher position than the second condenser and then drop to the receiver, to ensure a good flow. This could be used for a higher temperature for heat recovery, with the first condenser.
    In parallel, it is easier to modulate the condenser with the load fluctuation. The pressure drop through each condenser do not add up. It might take less refrigerant. But insure an equalizing line in between each condenser to insure good flow, and pay attention to the drop leg to the receiver versus pressure drop, if the condenser are not install at the same level and do not have the same load capacity.
    Kathleen, P.eng
    www.refri-ozone.com