    Jun 2014
    india
    22
    Two condenser use
    Hi... can we use two shell tube type condenser on single reciprocating compressor? Plz give me inlet and outlet hedders drawing
    Sep 2009
    Iran
    61
    500
    13
    Re: Two condenser use
    hi
    Jun 2014
    india
    22
    A drawing series connection other perlal connection witch the best
    Sep 2009
    Iran
    61
    500
    13
    is it depend's on conection sizes
    if your conection is small do parallel if not and you have enough room to put one of them on top of that do series
    on those have same capacity
    in parallel if one of them got leaks you could used other one for short periods
    Jan 2006
    Croatia
    63
    2,148
    Hi, manmohan ...
    Quote Originally Posted by manmohan View Post
    it is possible ...
    what is the main reason to use two condensers ... just curious ;-)
    ... in general it is better to connect condensers in parallel ...
    Best regards, Josip
    Jan 2002
    Canada
    35
    Hi Mammohan
    Some tips, If you design
    In serie, just take for account that the pressures losses through each condenser as to be added. Which increase the head pressure, and then decrease the overall efficiency. The second condenser might run often flooded if you have load fluctuation. Insure that the first condenser is located at a higher position than the second condenser and then drop to the receiver, to ensure a good flow. This could be used for a higher temperature for heat recovery, with the first condenser.
    In parallel, it is easier to modulate the condenser with the load fluctuation. The pressure drop through each condenser do not add up. It might take less refrigerant. But insure an equalizing line in between each condenser to insure good flow, and pay attention to the drop leg to the receiver versus pressure drop, if the condenser are not install at the same level and do not have the same load capacity.
    Kathleen, P.eng
    www.refri-ozone.com