Not sure what the Letters jumbled stuff is, but anyway. I did buy one, not sure if I did the right thing here but I bought...
DAIKIN INVERTER R410A SPLIT SERIES
FTXS25CVMB WALL INTERNAL WALL MOUNTED UNIT
RXS25CVMB OUTSIDE UNIT
AIR PURIFYING FILTER
REMOTE CONTROL & HOLDER
AVAILABLE FEATURES INCLUDE
AUTO.DRY.COOL.HEAT.FAN
OUTDOOR UNIT SILENT OPERATION TIMER & HOME LEAVE OPERATION
Looks like it will be a flared connection afterall.
Spec can be seen at...
http://www.easyventilation.com/image...unted_spec.pdf
-
18-06-2006, 06:45 PM #2
Re: Advice on Inverter Purchase/Install
DAIKIN INVERTER R410A SPLIT SERIES
FTXS25CVMB WALL INTERNAL WALL MOUNTED UNIT
RXS25CVMB OUTSIDE UNIT
AIR PURIFYING FILTER
REMOTE CONTROL & HOLDER
AVAILABLE FEATURES INCLUDE
AUTO.DRY.COOL.HEAT.FAN
OUTDOOR UNIT SILENT OPERATION TIMER & HOME LEAVE OPERATION
But these don't come with quick couplers on the pipework. You will need to pressure test and vacuum before opening the stop valves.
-
18-06-2006, 09:40 PM #3
Re: Advice on Inverter Purchase/Install
I will pick this up in a couple of days. When I get a chance to look at it I will sort a position out for the outside unit. I may get some brackets and fix it higher up on the wall to minimise ingress of dust.
I am still undecided as to it serving the lounge or bedroom.
I am a lot happier with the flared connection too.
I have been reminded by SWMBO that I have a number of jobs to complete before I start this one.
The spec does not give the length of the interconnecting cable, but I assume it can be extended.
Once mounted and wired I will be looking for an engineer to Vac down and check final gas pressure.
-
19-06-2006, 07:08 PM #4
Re: Advice on Inverter Purchase/Install
Originally Posted by mick2me
You dont get interconnecting cable with a proper split like you have bought, but you will need some 4-core 1.5mm.
If your using an isolator on the indoor unit then dont break the number 3. (comms)
-
19-06-2006, 09:16 PM #5
Re: Advice on Inverter Purchase/Install
If your using an isolator on the indoor unit then dont break the number 3. (comms)
Also important is to make sure that you have a good neutral otherwise you will blow the inverter board at switch on.
-
19-06-2006, 09:24 PM #6
Re: Advice on Inverter Purchase/Install
As already pointed out good choice of unit, the only thing i can throw in to the thread is i would recommend that you cut off the indoor flare nuts and braze the connections, makes a far neater job!
-
20-06-2006, 12:12 AM #7
Re: Advice on Inverter Purchase/Install
Thanks
The electrical advice will mean more to me when I see the manual. The Piping side will be dealt with by an engineer. I hope to collect it towards the end of the week.
-
30-06-2006, 05:41 PM #8
Re: Advice on Inverter Purchase/Install
Originally Posted by puddleboy3
Always braze the back of wall units, it takes 10 Min's max and will provide the customer with a proper job
-
11-07-2006, 10:50 PM #9
Re: Advice on Inverter Purchase/Install
Originally Posted by frank
Putting it through the Isolator?
I am running the 2.5mm T&E feed to the inverter back entry into a 20A rotary disconnector
Breaking live and neutral, bottom exit via flexible conduit to feed the inverter. The 1.5mm 3 core and earth leaves the inverter by the same flexible conduit, to the switch box, but is not broken by the switch. It just exits through the back of the switch into the house, running up the wall inside before rejoining the pipework on its route to the interior unit.
This allows the use of light Twin & Earth, and 3 Core and earth cable as opposed to Armoured cable.
Are you saying that running the control cable through the isolator will cause some kind of interferance?
Similar Threads
-
Inverter systems
By Latte in forum The Trail of TearsReplies: 23Last Post: 11-07-2007, 12:14 AM -
strange inverter problem
By rbartlett in forum Air ConditioningReplies: 11Last Post: 19-05-2006, 08:31 PM -
Advice for newbie - please be kind..!
By electricstuff in forum Air ConditioningReplies: 11Last Post: 04-10-2004, 06:52 PM -
A/C Inverter
By Jai in forum Air ConditioningReplies: 2Last Post: 06-11-2001, 01:24 AM