    Advice on Inverter Purchase/Install



    Can anyone advise on this.
    I have been looking at the Mitsubishi SRK**ZD Units.

    I intend to do all the heavy work of installing the units, pipe runs and electrics, then get a refrigeration engineer to vac out and commission the units.

    Any advice on Mitsubishi or alternative units would be appreciated.

    Am I right for going with a unit with 410a?



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Advice on Inverter Purchase/Install

    Welcome Mick, sparkies always

    Using R410a seems the way to go now, it does make the units a bit smaller for the output so there is a gain there.

    Can understand your suggestion of installing yourself but have to ask the question:- Do you know how to braze and the requirements for doing refrigeration pipework?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    May 2006
    Location
    Isle of Wight, Uk
    Age
    47
    Posts
    424
    Rep Power
    20

    Re: Advice on Inverter Purchase/Install

    Good choice of unit, great performance and value for money. Ive just ordered one for myself -just a standard srk40hd though.
    Only down side is that on the smaller units - up to srk50
    wiring the interconnect when machine is on the wall is a real pain in the wotsit.
    R410a not a problem if right tools and methods used.

    No offence Mick, but over the years I have noticed that sparkies and a/c systems don't mix well !

    Good luck anyway mate

  4. #4
    Join Date
    May 2006
    Location
    Nottingham
    Age
    72
    Posts
    163
    Rep Power
    18

    Re: Advice on Inverter Purchase/Install

    Thanks for the welcome and prompt replies.

    In a former life I installed Freezers and cold rooms for a large food chain in the midlands. The rerigeration side was dealt with by our fridge engineers.

    Are you saying that these units will require some brazing work? (If so the engineer could do this.) I thought they would be flared at both ends of the pipes?

    Also I have read that the pipes need connecting by means of a torque wrench, is this true?

    There are easy fit units, that I have considered, with clip together flexible pipes, but I am not sure how good the actual AC units are themselves.
    Last edited by mick2me; 13-06-2006 at 12:07 AM.

  5. #5
    Join Date
    May 2006
    Location
    Nottingham
    Age
    72
    Posts
    163
    Rep Power
    18

    Talking Re: Advice on Inverter Purchase/Install

    Quote Originally Posted by Andy AC
    Good choice of unit, great performance and value for money. Ive just ordered one for myself -just a standard srk40hd though.
    Only down side is that on the smaller units - up to srk50
    wiring the interconnect when machine is on the wall is a real pain in the wotsit.
    R410a not a problem if right tools and methods used.

    No offence Mick, but over the years I have noticed that sparkies and a/c systems don't mix well !

    Good luck anyway mate
    Andy

    I noticed the same thing with plumbers

    I did struggle to find many suppliers for the SRK or similar units, so that I can shop around.

    I will get the supplier to make up the pipes to my measurements, when I order the units.

  6. #6
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Advice on Inverter Purchase/Install

    Mick, if you are installing with a short pipe run, less than the length of a coil of copper then you could get away without brazing any joints.

    R410a does require dedicated flaring tools and the use of a torque wrench.

    I will get the supplier to make up the pipes to my measurements
    That is always an option assuming that they will do that for you.
    Last edited by Brian_UK; 13-06-2006 at 10:39 PM. Reason: Spelling, again!!
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  7. #7
    Join Date
    May 2006
    Location
    Nottingham
    Age
    72
    Posts
    163
    Rep Power
    18

    Re: Advice on Inverter Purchase/Install

    Thanks Brian

    So brazing is for Pipe joining.
    I expect the pipe run to be no more than 5-6 metres.
    So just flared connections?

    Reading the requirements for installing units that run on R410a is an eye opener!

    http://www.bdt.co.nz/comfortmaster/d...410a_guide.pdf

  8. #8
    Join Date
    May 2006
    Location
    Sussex
    Posts
    362
    Rep Power
    20

    Re: Advice on Inverter Purchase/Install

    Suggest:
    a) Make sure you keep the pipe ends sealed with some tape to prevent moisture getting inside, until the fridge engineer shows up to make the unit connections etc.

    b) Read the install manual as to required space around the units when mounting them.

  9. #9
    Join Date
    May 2006
    Location
    Nottingham
    Age
    72
    Posts
    163
    Rep Power
    18

    Re: Advice on Inverter Purchase/Install

    Quote Originally Posted by Makeit go Right
    Suggest:
    a) Make sure you keep the pipe ends sealed with some tape to prevent moisture getting inside, until the fridge engineer shows up to make the unit connections etc.

    b) Read the install manual as to required space around the units when mounting them.
    Thank you

    Any advice on how good these are?
    They say "Flexible lines. No vacuum pump or engineer required for installation."?


  10. #10
    Join Date
    May 2006
    Location
    Leicestershire
    Age
    58
    Posts
    28
    Rep Power
    0

    Re: Advice on Inverter Purchase/Install

    mick if your going to use the above flexi pipes make sure you wear gloves and can push the pipes on with considerable force as they tend to loose refrigerant.

  11. #11
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Advice on Inverter Purchase/Install

    Forgive the question Mick but are those flexi pipe suggested for use with R410a?

    Also, does the a/c unit come with the correct fittings to accept those pipes?

    Any flexi pipe I would consider dubious for use on R410a due to the higer working pressures involved, a proper brazed or flared joint every time.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  12. #12
    Join Date
    May 2006
    Location
    Nottingham
    Age
    72
    Posts
    163
    Rep Power
    18

    Re: Advice on Inverter Purchase/Install

    Quote Originally Posted by Brian_UK
    Forgive the question Mick but are those flexi pipe suggested for use with R410a?

    Also, does the a/c unit come with the correct fittings to accept those pipes?

    Any flexi pipe I would consider dubious for use on R410a due to the higer working pressures involved, a proper brazed or flared joint every time.
    I thought the same Brian, being aware of the Pressure of 410a.

    But here is the spec sheet for a 'Quick Couple' 410 inverter.

    http://global-cooling.co.uk/aircondi...cification.pdf

  13. #13
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Advice on Inverter Purchase/Install

    Thanks Mick, I stand corrected, bemused but advised
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  14. #14
    Join Date
    May 2006
    Location
    Nottingham
    Age
    72
    Posts
    163
    Rep Power
    18

    Re: Advice on Inverter Purchase/Install

    You've got me wondering how good these connections are. I dont see how you can connect them without a small amount of air getting into the system. And what effect would that have?

    There must be a lot of people installing these systems from DIY stores.

  15. #15
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Advice on Inverter Purchase/Install

    Having a closer look at those quick couplers and it does look as though they are made a bit stronger than the ones we may all have been thinking of.

    The older ones, R22 etc, were simply a screwed connector, male/female ends of course, with a thin metal seal over the pipe ends. You had to start the threads and then crank up the spanners as fast as you could !! You didn't normally have any air gettting into the system because you were busy losing gas through the joints that you were frantically trying to do up.

    The joints shown in your picture seem to have a more psoitive action. It looks like you push the female pipe end into the male unit socket and perhaps lock it together somehow.

    The lever by the guys left hand seems to have a cam attached which will make the final connection thereby breaking the pipe seals and closing the joint.

    Mind you, you won't find them on a Mitsi
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  16. #16
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Advice on Inverter Purchase/Install

    The joints shown in your picture seem to have a more psoitive action.
    Hi Brian

    Are you just testing the other Brian's theory about the letters being jumbled up

  17. #17
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Advice on Inverter Purchase/Install

    No Frank, I've just spotted it myself and was about to correct when I saw your post.

    Now I don't know whether to correct or not; I had better leave it otherwise your post will look as bad as mine
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  18. #18
    Join Date
    May 2006
    Location
    Nottingham
    Age
    72
    Posts
    163
    Rep Power
    18

    Re: Advice on Inverter Purchase/Install

    Not sure what the Letters jumbled stuff is, but anyway. I did buy one, not sure if I did the right thing here but I bought...

    DAIKIN INVERTER R410A SPLIT SERIES


    FTXS25CVMB WALL INTERNAL WALL MOUNTED UNIT

    RXS25CVMB OUTSIDE UNIT
    AIR PURIFYING FILTER
    REMOTE CONTROL & HOLDER


    AVAILABLE FEATURES INCLUDE
    AUTO.DRY.COOL.HEAT.FAN
    OUTDOOR UNIT SILENT OPERATION TIMER & HOME LEAVE OPERATION

    Looks like it will be a flared connection afterall.

    Spec can be seen at...
    http://www.easyventilation.com/image...unted_spec.pdf

  19. #19
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Advice on Inverter Purchase/Install

    DAIKIN INVERTER R410A SPLIT SERIES


    FTXS25CVMB WALL INTERNAL WALL MOUNTED UNIT

    RXS25CVMB OUTSIDE UNIT
    AIR PURIFYING FILTER
    REMOTE CONTROL & HOLDER


    AVAILABLE FEATURES INCLUDE
    AUTO.DRY.COOL.HEAT.FAN
    OUTDOOR UNIT SILENT OPERATION TIMER & HOME LEAVE OPERATION
    Good Choice.

    But these don't come with quick couplers on the pipework. You will need to pressure test and vacuum before opening the stop valves.

  20. #20
    Join Date
    May 2006
    Location
    Nottingham
    Age
    72
    Posts
    163
    Rep Power
    18

    Re: Advice on Inverter Purchase/Install

    I will pick this up in a couple of days. When I get a chance to look at it I will sort a position out for the outside unit. I may get some brackets and fix it higher up on the wall to minimise ingress of dust.

    I am still undecided as to it serving the lounge or bedroom.

    I am a lot happier with the flared connection too.

    I have been reminded by SWMBO that I have a number of jobs to complete before I start this one.

    The spec does not give the length of the interconnecting cable, but I assume it can be extended.

    Once mounted and wired I will be looking for an engineer to Vac down and check final gas pressure.

  21. #21
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Advice on Inverter Purchase/Install

    Frank, you must be getting telepathic, you can sell from afar now
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  22. #22
    Join Date
    Dec 2005
    Location
    Cheshire
    Age
    39
    Posts
    264
    Rep Power
    21

    Smile Re: Advice on Inverter Purchase/Install

    Quote Originally Posted by mick2me
    I will pick this up in a couple of days. When I get a chance to look at it I will sort a position out for the outside unit. I may get some brackets and fix it higher up on the wall to minimise ingress of dust.

    I am still undecided as to it serving the lounge or bedroom.

    I am a lot happier with the flared connection too.

    I have been reminded by SWMBO that I have a number of jobs to complete before I start this one.

    The spec does not give the length of the interconnecting cable, but I assume it can be extended.

    Once mounted and wired I will be looking for an engineer to Vac down and check final gas pressure.

    You dont get interconnecting cable with a proper split like you have bought, but you will need some 4-core 1.5mm.

    If your using an isolator on the indoor unit then dont break the number 3. (comms)

  23. #23
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Advice on Inverter Purchase/Install

    If your using an isolator on the indoor unit then dont break the number 3. (comms)
    Good advice . Certainly don't put it through the isolator where it could pick up interference. (Crimp it seperately).

    Also important is to make sure that you have a good neutral otherwise you will blow the inverter board at switch on.

  24. #24
    Join Date
    Mar 2006
    Location
    Glasgow, Scotland
    Posts
    177
    Rep Power
    19

    Re: Advice on Inverter Purchase/Install

    As already pointed out good choice of unit, the only thing i can throw in to the thread is i would recommend that you cut off the indoor flare nuts and braze the connections, makes a far neater job!

  25. #25
    Join Date
    May 2006
    Location
    Nottingham
    Age
    72
    Posts
    163
    Rep Power
    18

    Re: Advice on Inverter Purchase/Install

    Thanks

    The electrical advice will mean more to me when I see the manual. The Piping side will be dealt with by an engineer. I hope to collect it towards the end of the week.

  26. #26
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Advice on Inverter Purchase/Install

    Glad that it's all coming together for you Mick.

    Just follow good electrical practice, as you would, and you shouldn't have any problems.

    In this case you have to think about your own safety as you are your own customer
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  27. #27
    Join Date
    May 2006
    Location
    Nottingham
    Age
    72
    Posts
    163
    Rep Power
    18

    Re: Advice on Inverter Purchase/Install

    Quote Originally Posted by Brian_UK
    Glad that it's all coming together for you Mick.

    Just follow good electrical practice, as you would, and you shouldn't have any problems.

    In this case you have to think about your own safety as you are your own customer
    Thanks Brian.

    The four core 1.5 cable (or 2.00mm if over 10m)
    I have got to sort? Having read online manual I see
    the no 3 connecting wire and reason for not isolating it. LIve Neutral Earth Signal.

    I may collect the unit tonight or tomorrow.
    There will be no doubt more Q's then

    Ta'
    Mick T.

  28. #28
    Join Date
    May 2006
    Location
    Norwich
    Age
    53
    Posts
    134
    Rep Power
    18

    Re: Advice on Inverter Purchase/Install

    Quote Originally Posted by puddleboy3
    As already pointed out good choice of unit, the only thing i can throw in to the thread is i would recommend that you cut off the indoor flare nuts and braze the connections, makes a far neater job!
    yep cant agree more, the connection to the inside unit MUST be brazed, we always Braze these as they are always either behind the unit or halfway through a wall, we have been called to many ( other installs) where these have not been brazed and had to take the whole wall unit down , braze and re install costing the customer a small fortune


    Always braze the back of wall units, it takes 10 Min's max and will provide the customer with a proper job

  29. #29
    Join Date
    May 2006
    Location
    Nottingham
    Age
    72
    Posts
    163
    Rep Power
    18

    Re: Advice on Inverter Purchase/Install

    Thanks for that.

    Are we saying that the connection on the indoor unit is not reliable?

    Brazing does that mean that the pipes need to be charged with nitrogen?

    Anyways I picked the Daikin Inverter unit up last week, and am very pleased with the quality of the units.

    First question on this is regarding the pipe.

    Daikin specify
    GAS OD 9.5 mm
    liquid OD 6.4 mm
    thickness 0.8 mm

    I know someone who has a coil of
    1/4 X 22G- 6.35 X 0.71MM
    Is this suitable?

    Also Other sizes I have seen listed are Imperial?
    1/4" 3/8" 1/2" 5/8"

    Are there imperial sizes and metric?

    What do I buy for the Daikin spec pipe?

    Thanks

  30. #30
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Advice on Inverter Purchase/Install

    Normal refrigeration quality 1/4" and 3/8" pipework will be fine.

    Don't get concerned about having to braze the indoor connections, it's not compulsory and the flare joints are OK if made correctly - some engineers prefer to cut off the flares and make a brazed joint. I do it too when the flares would end up in to the wall with no future access.

    As you intend to get a fridge guy in to vac out and commission why don't you get him to make the flares?

  31. #31
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: Advice on Inverter Purchase/Install

    Quote Originally Posted by frank
    Normal refrigeration quality 1/4" and 3/8" pipework will be fine.

    Don't get concerned about having to braze the indoor connections, it's not compulsory and the flare joints are OK if made correctly - some engineers prefer to cut off the flares and make a brazed joint. I do it too when the flares would end up in to the wall with no future access.

    As you intend to get a fridge guy in to vac out and commission why don't you get him to make the flares?
    Hi

    in defense of flares the new offset rotary flaring gear is great, you don't even ream the pipe and provided your cutters are sharp the flare comes out like a machined flare

    I will confess if the flare is hard to get at I would smear high strength lock tight on the flare mating surface, it will never leak, but be careful don't use too much, my mate says I block gomex fittings

    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes:

  32. #32
    Join Date
    May 2006
    Location
    Nottingham
    Age
    72
    Posts
    163
    Rep Power
    18

    Re: Advice on Inverter Purchase/Install

    Thanks Frank & Andy.

    I checked the indoor Unit for the first time today.
    The pipes come out of the right hand side looking from the front. They terminate in the center of the unit, which is where the joint will be. If I take the pipe run in through the left hand side of the unit, there will be access to the joints by lifting the inside unit off its mounting plate.

    I was suprised to see that both pipes ran in one insulation sleeve? Surely isnt one very hot and the other cold. Should they not be thermally insulated from one another?

    Talking of getting an engineer?
    I will make that subject of another thread post.
    By which you may or may not be suprised!

  33. #33
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Advice on Inverter Purchase/Install

    Talking of getting an engineer?
    You did in your first post.
    I intend to do all the heavy work of installing the units, pipe runs and electrics, then get a refrigeration engineer to vac out and commission the units.

  34. #34
    Join Date
    May 2006
    Location
    Nottingham
    Age
    72
    Posts
    163
    Rep Power
    18

    Re: Advice on Inverter Purchase/Install

    No, Frank I met an engineer the other day.

    Here is my experience!

    http://www.refrigeration-engineer.co...ead.php?t=5160

  35. #35
    Join Date
    May 2006
    Location
    Nottingham
    Age
    72
    Posts
    163
    Rep Power
    18

    Re: Advice on Inverter Purchase/Install

    Quote Originally Posted by Brian_UK

    R410a does require dedicated flaring tools and the use of a torque wrench.
    Can someone explain this.

    Is it a different shape of flare?

    And what type of Tork wrench is used for the nut?

  36. #36
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Advice on Inverter Purchase/Install

    In theory you are flaring a slightly thicker pipe wall and the tool allows for this by 'forming' the flare not just squeezing the flare shape out of the pipe.

    The torque wrench is an open ended spanner head that fits into the torque wrench handle. The handle will 'snap' at the correct setting.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  37. #37
    Join Date
    May 2006
    Location
    Nottingham
    Age
    72
    Posts
    163
    Rep Power
    18

    Re: Advice on Inverter Purchase/Install

    Quote Originally Posted by Brian_UK
    In theory you are flaring a slightly thicker pipe wall and the tool allows for this by 'forming' the flare not just squeezing the flare shape out of the pipe.

    The torque wrench is an open ended spanner head that fits into the torque wrench handle. The handle will 'snap' at the correct setting.
    Thanks Brian, in my research I have never seen a flaring tool that specifies that it is suitable for 410 or a thicker grade of pipe?.

  38. #38
    Join Date
    May 2006
    Location
    Nottingham
    Age
    72
    Posts
    163
    Rep Power
    18

    Re: Advice on Inverter Purchase/Install

    Quote Originally Posted by frank
    Good advice . Certainly don't put it through the isolator where it could pick up interference. (Crimp it seperately).
    Now I am wondering if I am reading this right?

    Putting it through the Isolator?

    I am running the 2.5mm T&E feed to the inverter back entry into a 20A rotary disconnector



    Breaking live and neutral, bottom exit via flexible conduit to feed the inverter. The 1.5mm 3 core and earth leaves the inverter by the same flexible conduit, to the switch box, but is not broken by the switch. It just exits through the back of the switch into the house, running up the wall inside before rejoining the pipework on its route to the interior unit.

    This allows the use of light Twin & Earth, and 3 Core and earth cable as opposed to Armoured cable.

    Are you saying that running the control cable through the isolator will cause some kind of interferance?

  39. #39
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Advice on Inverter Purchase/Install

    I think he is saying that you shouldn't put the control wire through the switch contacts, "crimp it". Ideally the control and power wires could be separated but in practice very rarely are.

    However if you put them through a switch the line quality can fall and the signal gets corrupted. Depending on the make etc the control signal may be a modulated 12vdc or a modulated 120v or a carrier low voltage, so any break in the line can cause problems.

    PS see other thread for flaring data
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  40. #40
    Join Date
    May 2006
    Location
    Nottingham
    Age
    72
    Posts
    163
    Rep Power
    18

    Question Re: Advice on Inverter Purchase/Install

    Quote Originally Posted by Brian_UK
    I think he is saying that you shouldn't put the control wire through the switch contacts, "crimp it". Ideally the control and power wires could be separated but in practice very rarely are.

    However if you put them through a switch the line quality can fall and the signal gets corrupted. Depending on the make etc the control signal may be a modulated 12vdc or a modulated 120v or a carrier low voltage, so any break in the line can cause problems.
    The three core & earth will pass straight through the switch box without breaking the conductor, conductor insulation, or outer cable insulation. Though it will run parallel to the 2.5mm power supply cable for about a metre, and passes close by the switch (which would only be operated under emergency conditions).

    As the entire lenghts of the three core & earth interior unit feed, will carry 240v parallel to the signal cable, I cant see it causing any more intereference passing it through the switch?

    Im just wondering where running a signal cable alongside 240v cores fits with the IEE regs?

  41. #41
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Advice on Inverter Purchase/Install

    Quote Originally Posted by mick2me
    Im just wondering where running a signal cable alongside 240v cores fits with the IEE regs?
    Sorry, have the Japanese read the IEE Regs

    Honestly there are very rarely problems on splits, it can be more sensitive on the VRF/VRV type kit because the data list and flow is probably greater.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  42. #42
    Join Date
    Jun 2006
    Location
    Ohio
    Posts
    18
    Rep Power
    0

    Re: Advice on Inverter Purchase/Install

    Yeah you pickup about 5% capacity fo rthe same physical size unit, and at a higher SEER rating. Drawback is , its like a loaded gun at the pressures it runs. JMO,

  43. #43
    Join Date
    May 2006
    Location
    Nottingham
    Age
    72
    Posts
    163
    Rep Power
    18

    Re: Advice on Inverter Purchase/Install

    Quote Originally Posted by Brian_UK
    Sorry, have the Japanese read the IEE Regs
    Yes, Silly Me!
    Last edited by mick2me; 11-07-2006 at 11:53 PM.

  44. #44
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Advice on Inverter Purchase/Install

    Quote Originally Posted by Brian_UK
    I think he is saying that you shouldn't put the control wire through the switch contacts, "crimp it". Ideally the control and power wires could be separated but in practice very rarely are.

    However if you put them through a switch the line quality can fall and the signal gets corrupted. Depending on the make etc the control signal may be a modulated 12vdc or a modulated 120v or a carrier low voltage, so any break in the line can cause problems.
    Exactly Brian

    BS7671 recommend a minimum seperation of 300mm between data and power cables but in practice this isn't possible on an split install. Just don't put the data cable through the switch contacts.

  45. #45
    Join Date
    May 2006
    Location
    Nottingham
    Age
    72
    Posts
    163
    Rep Power
    18

    Re: Advice on Inverter Purchase/Install

    Just a point about Earth Bonding.

    I intend to run a 6mm bonding cable from the consumer unit via the flexible conduit, and earth bond the brackets and inverter assembly.
    Any comments on 'Equipotential Bonding' ?

  46. #46
    Join Date
    May 2006
    Location
    Nottingham
    Age
    72
    Posts
    163
    Rep Power
    18

    Thumbs up Re: Advice on Inverter Purchase/Install

    Quote Originally Posted by TopMechanic
    Yeah you pickup about 5% capacity fo rthe same physical size unit, and at a higher SEER rating. Drawback is , its like a loaded gun at the pressures it runs. JMO,
    Efficient, Powerful, and a novel method of committing suicide

  47. #47
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Advice on Inverter Purchase/Install

    Quote Originally Posted by mick2me
    Just a point about Earth Bonding.

    I intend to run a 6mm bonding cable from the consumer unit via the flexible conduit, and earth bond the brackets and inverter assembly.
    Any comments on 'Equipotential Bonding' ?
    Why?

    The CPC within your T&E will be sufficient and the whole casing will be connected to it, therefore, so will your brackets (and the missus when she touches it ).
    Equipotential bonding ensures that all metallic parts are at the same potential. Unless you are installing seperate traywork for your cables/pipes to run on then you don't need a seperate earth.

  48. #48
    Join Date
    May 2006
    Location
    Nottingham
    Age
    72
    Posts
    163
    Rep Power
    18

    Re: Advice on Inverter Purchase/Install

    Quote Originally Posted by frank
    Why?

    The CPC within your T&E will be sufficient and the whole casing will be connected to it, therefore, so will your brackets (and the missus when she touches it ).
    Equipotential bonding ensures that all metallic parts are at the same potential. Unless you are installing seperate traywork for your cables/pipes to run on then you don't need a seperate earth.
    Exactly, Pointless, Bonding items together via cable link, that are themselves physically bonded together, and already a good conductor of electricity.

    Bonding Soldered pipework a good example.
    OTT but required by the said regs? (perhaps not 'Big in Japan')

    However, as I have the cable and the clips, and it will take 5 mins, I will do it. It will look good on any inspection.

    "Bull**!t", I call it!

  49. #49
    Join Date
    Dec 2005
    Location
    Cheshire
    Age
    39
    Posts
    264
    Rep Power
    21

    Re: Advice on Inverter Purchase/Install

    Mick are you getting an engineer to do all the pipework, pressure testing etc and when??

  50. #50
    Join Date
    May 2006
    Location
    Nottingham
    Age
    72
    Posts
    163
    Rep Power
    18

    Re: Advice on Inverter Purchase/Install

    I have changed the run of pipes now. Its much simpler run, One 90 bend at the Inverter one at the wall. Not a problem for me to pull the pipes in now, with the aid of a bending spring. Just like Pyro, anyone remember that?

    However extesive reading here and elswhere, has convinced me that flaring pipe, ensuring leakproof system and vaccing out are a professionals job.

    I am (or was) a sparky, mate, so, feel competant to mount units and do the electrics. In fact all the bits I do are probably overkill, doubling up on fixings, earthing bits that probably dont need earthing etc.

    I am nowhere near that stage yet, as I have had to have the (stainless steel) brackets cut and drilled by an engineering firm.

Page 1 of 2 12 LastLast

Similar Threads

  1. Inverter systems
    By Latte in forum The Trail of Tears
    Replies: 23
    Last Post: 11-07-2007, 12:14 AM
  2. strange inverter problem
    By rbartlett in forum Air Conditioning
    Replies: 11
    Last Post: 19-05-2006, 08:31 PM
  3. Advice for newbie - please be kind..!
    By electricstuff in forum Air Conditioning
    Replies: 11
    Last Post: 04-10-2004, 06:52 PM
  4. A/C Inverter
    By Jai in forum Air Conditioning
    Replies: 2
    Last Post: 06-11-2001, 01:24 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •