    Oct 2008
    newbury
    1,403
    30
    Daikin twin not ramping up on heating
    Chaps
    got a 4kw twin split 2012.
    both indoors run on cooling as normal. but on heating the unit will only ramp up to 240psig and hence no real heat effect
    The refrigerant charge is correct so I'm thinking it's possibly sensor ?
    suggestions etc
    richard
    (not always sunny Tenerife)
    Oct 2003
    5,540
    29
    Re: Daikin twin not ramping up on heating
    Hi Richard,
    Can this help?
    http://www.refrigeration-engineer.co...not-ramping-up
    Peter (This morning everything covered with snow and -3C)
    PS: Is your back healed again?
    Dec 2008
    522
    Make and model please might give us a little more of a clue.
    5,134
    43
    Hi Richard
    It could be the indoor coil sensor or the outdoor discharge thermistor out of calibration.
    In cooling mode, the indoor sensor is used for freeze up protection, but in heating, it is used for holding off the indoor fan until the coil temp is above 34C to prevent cold draughts. In the meantime, the compressor will hang back waiting for the indoor signal to ramp up.
    If the compressor discharge thermistor is reading incorrectly then the unit will prevent the compressor ramping up due to discharge protection control.
    Attached Files Attached Files
    I'm back on the Pale
    Oct 2003
    5,540
    29
    With this free app from Daikin, you can find the resistance values
    Without this app, I can't service a VRV :-)
    https://play.google.com/store/apps/d...n.aircon&hl=nl
    Oct 2008
    newbury
    1,403
    30
    Returned to site today.
    Thought I'd go through a run again before pulling it apart.. As you'd expect both indoor units ramped up to full heating. 45 minutes later everything worked as normal
    Left alone till the next time it fails
    Thanks to all.