Thread: Oil Type for HSN
18-12-2018, 12:02 PM #1
- Sep 2009
- Iran
- 66
- 672
- 1
- 19
Oil Type for HSN
In bitzer document for R=404A has BSE 170
pour point of this oil =-28
if we want ti run Evaporator SST = -45
Condenser SDT = +45
still document is showing BSE 170
can we use SL 32
Pour point = -48
thanks
MBC
31-01-2019, 04:02 PM #2
- Sep 2009
- Iran
- 66
- 672
- 1
- 19
Re: Oil Type for HSN
waiting for reply.
31-01-2019, 05:58 PM #3
Bitzer document uses BS170 over range +7.5°C to -50°C
Check docs here https://www.bitzer.de/gb/en/document...lng=en&lang=enBrian - Newton Abbot, Devon, UK
31-01-2019, 06:33 PM #4
Hi if you use thin oil, it won't seal the screws properly to pump,
31-01-2019, 08:24 PM #5
- Sep 2009
- Iran
- 66
- 672
- 1
- 19
pour point of BSE 170 is about - 28
our SSD is - 45 and Evaporator working all the time
( O2) system and we do not have a defrost to return oil
I looked the docs in Bitzer it wrote BSE 170
I put mail to them Bitter but ......
some thing is not right
01-02-2019, 12:13 AM #6
If you do not trust the manufacturer then you wont trust anyone else.
01-02-2019, 02:20 AM #7
01-02-2019, 09:51 AM #8
- Sep 2009
- Iran
- 66
- 672
- 1
- 19
Dear Brian
I trust them and read all of docs in there's sits
But I put this question to them
first they wrote oil should be BSE 170
When I told them about pour point they mailed me BSE32
I did a lots work with HSN and used BSE 170
( more than 60 cold rooms )
But all of them was cold rooms ( -35 c) with defrost system
this one has not defrost so I am not sure about type of oil
for R 134A they wrote -25 c
01-02-2019, 10:51 AM #9
From My experience with Bitzer, Do not use any other oil.
What is the compressor model?
01-02-2019, 01:22 PM #10
- Sep 2009
- Iran
- 66
- 672
- 1
- 19
It is HSN 7471-75
with ECO
SST = -45
SDT= 45
R 404 A
Before I used R 22 and oil were B100 it is mineral oil
now I am going to use R 404 A
02-02-2019, 11:30 AM #11
hi mbc,
when you are reading the oil specifications, "In bitzer document for R=404A has BSE 170
pour point of this oil =-28" >>> these -28 are for pure oil.
in your system, refrigerant is mixed with oil and there is no problem in using BSE 170 at low temperatures.
using iso32 oil you will get a high refrigerant concentration in oil at HP stage, low oil viscosity, and bad lubrification at bearings.