    30gtn



    Good morning All.
    Can someone assist please.
    I have this 30gtn carrier chiller, it trips breaker immediately it wanted to start running.
    I have checked all Fan Motor and Compressor for Short and they are ok.
    Only one compressor is bad and I have disconnected it from the system.
    All relays have been checked.
    Please can someone assist me on what to do. Thanks



  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: 30gtn

    Your Earlier posts say it all Charles.
    Good day Engineers
    Please I need urgent help.
    I'm not that grounded in electrical.

    I connected a compressor today and the result was a blast.. Breakers trip and compressor burnt.


    what you are now getting I assume?
    Is as a direct result of your previous actions.

    Knowing when to stop is sometimes as important as knowing what to do.

    Enlist the help of local more knowledgeable colleagues.



    Grizzly
    Last edited by Grizzly; 31-12-2018 at 11:26 AM.
    Despite the High Cost of Living it still remains Popular!

  3. #3
    Join Date
    Jun 2016
    Location
    Nigeria
    Posts
    64
    Rep Power
    8

    Re: 30gtn

    Grizzly good pm,
    Though I'm not grounded in electrical but I understand it because I read and learn everyday.
    I only asked questions because I want to know more.
    I was expecting someone who has experience same problem to tell me the possible causes.

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: 30gtn

    You've checked for shorts but have you checked the starters?

    Is the supply voltage correct and strong enough?

    Switch off/remove fuses to the compressors etc. Start up and recheck the starters for continuity.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Jun 2006
    Location
    South Coast
    Posts
    278
    Rep Power
    23

    Re: 30gtn

    Get hold of Mandola's in Lagos as the local Carrier dealer they should be able to solve this problem. You seem out if your depth.

    Gibbo.

  6. #6
    Join Date
    Jun 2006
    Location
    South Coast
    Posts
    278
    Rep Power
    23

    Re: 30gtn

    Mandilas in Lagos.

  7. #7
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: 30gtn

    Check that your electric supply has 3 phases.
    You might have lost one when it tripped the first time.

  8. #8
    Join Date
    Jun 2016
    Location
    Nigeria
    Posts
    64
    Rep Power
    8

    Re: 30gtn

    Thanks a lot Mr Brian _UK

  9. #9
    Join Date
    Jun 2016
    Location
    Nigeria
    Posts
    64
    Rep Power
    8

    Re: 30gtn

    Thanks Mr Gibbo, I'm a staff of Mandilas Enterprises Limited. Carrier Division, Lagos

  10. #10
    Join Date
    Jun 2016
    Location
    Nigeria
    Posts
    64
    Rep Power
    8

    Re: 30gtn

    Chemi cool thanks a lot