    Panasonic HZ9RKE Heat pump



    Hi
    I have a 2016 heat pump and suddently it stopped, and i was able to get error code H97 out of it.

    From Google I see this means Outdoor fan motor - DC MOtor mechanisn locked

    The outdoor fan blades rotated fine by hand, so its not the motor seized up..

    Anyone seen this error before and can assist ?

    BR
    Daniel..



  2. #2
    Join Date
    Dec 2008
    Location
    UK
    Posts
    568
    Rep Power
    24

    Re: Panasonic HZ9RKE Heat pump

    This can often be either a fault in the fan motor or the inverter drive for the motor. Further investigation would be required to determine where the fault is.
    Mobile A/C at its best, see avatar.