Results 1 to 20 of 20
    Jun 2016
    Nigeria
    Delta connection
    Good day Engineers
    Please I need urgent help.
    I'm not that grounded in electrical.
    I connected a compressor today and the result was a blast.. Breakers trip and compressor burnt.
    The compressor was rewound while the 6 terminals connected with jumpers.
    Thus making it 3 lines to connect the 3 phase.
    My question is that can I connect the 3 phase from any side of the jumpers. That is either from 1, 2, 3 or 7, 8, 9
    70
    10,703
    52
    Re: Delta connection
    Split Croatia
    52
    6,118
    If compressor is burnt than that mean it was wrongly connected in first time. Give us picture of compressor nameplate and give us data of Nigerian voltages of 3 phase system. Then we will be able to help you to correctly connect compressor. Do not connect it in current jumper configuration since it will probably burn again!
    As I can see, your country have 400V 3 phase system.
    If motor nameplate say 230Δ/400Y than it could be connected only in star winding configuration, and delta is not option for your country, except if you using frequency inverter configured to run with 230V.
    In your country you can use delta configuration only with motors rated to run delta on 400V (400Δ/400Y or 400Δ/690Y)
    Now, when I am officialy citizen off EU, I am looking for decent job! For any job offer please check my profile!
    Jun 2016
    Nigeria
    Thanks a lot Mr. Nike.
    Going with your clear explanation, which says L1 to U1, L2 to V1, L3 to W1... What will happen if I mistakenly connect L1 to W2, L2 to U2 and L3 to V2.
    Referring to your Delta Connection Diagrams.
    Dec 2008
    522
    As U1 is linked out to W2 it does not really matter which terminal you connect L1 onto. It is just conventional to connect onto U1, V1 and W1.
    Jun 2016
    Nigeria
    Thanks hyperion
    Split Croatia
    52
    6,118
    Quote Originally Posted by OkonedoCharles View Post
    I think you missing point of my post which is reason why your motor is burnt in first place. I am not sure that you can connect your motor in delta configuration.
    But if you asking in general, than it makes no difference from which side of delta connection you supply power (U1,V1,W1 OR U2,V2,W2) as Hyperion already explained.
    Jun 2016
    Nigeria
    Thanks Mr. Nike!
    I got you. Though the connection I did was right, yet the Carlyle compressor winding got shortened to body.
    Again the ways the coils read to each other got me confused.
    Considering the terminal, T1, T2 and T3 all read to each other ( resistance), while T7 T8 and T9 also read continuity.
    Jumpers were used to link T1 to T7, T2 to T8, and T3 to T9.
    I was not expecting T1, T2 and T3 to read continuity, likewise T7, T8, T8.
    70
    10,703
    52
    Let us start again, this time from the motor starter.
    How is the motor started?
    Is it direct on line, star/delta, part wind ?
    Split Croatia
    52
    6,118
    By numbers mentioned (T1-T3, T7-T9) It is probably part winding motor! Where are T4-T6?
    That is why I asked first to:"Give us picture of compressor nameplate"!
    Jun 2016
    Nigeria
    Direct on line
    Jun 2016
    Nigeria
    IMG_20181218_115138.jpgIMG_20181218_115138.jpgIMG_20181218_115138.jpgIMG_20181218_115138.jpgIMG_20181218_115138.jpg
    Jun 2016
    Nigeria
    5,134
    43
    Here is a link to the 06E service Manual.
    https://www.utcccs-cdn.com/hvac/docs...06/020-611.pdf
    Electrical connections start around page 108
    I'm back on the Pale
    Jun 2016
    Nigeria
    Thanks a lot Mr. Frank
    470
    Hi looking at the compressor photo, it is a 50% part wind and your wiring is OK, I think it might be a problem with the stator or the rotor bars
    70
    10,703
    52
    Quote Originally Posted by GHAZ View Post
    Can you please explain how it is a part wind with the wiring scheme shown.
    Split Croatia
    52
    6,118
    Hi Brian!
    According to nameplate picture, motor is internally connected in star (or delta) configuration and cannot be in field modified.
    When connected 3 wire +PE with bridges, it is direct on-line start (2 windings in parallel => 100% starting current).
    When connected with 6 wires +PE without bridges, than it is part winding. In that case 2 contactors are used with one with time delay at start (1 separate winding at start for time delay => 50% starting current).
    As OP stated earlier, it was bridged as in picture at right side of motor nameplate which is direct on-line connection.
    But we still don't have full model number to verify correct voltage is applied. If compressor previously worked in Nigeria on direct line voltage, than it is probably of correct voltage.
    All that above said is under presumption that motor rewinding is done exactly as original is wounded in the factoy.
    Oct 2009
    184
    13
    How about a photo of the contactor(s)
    70
    10,703
    52
    Thanks Nike, I do understand the part wind scheme but was asking because the OP stated it was a DoL starter and I couldn't see how part wind could be applied that way.