    Sep 2009
    Iran
    66
    672
    1
    Oil Type for HSN
    In bitzer document for R=404A has BSE 170
    pour point of this oil =-28
    if we want ti run Evaporator SST = -45
    Condenser SDT = +45
    still document is showing BSE 170
    can we use SL 32
    Pour point = -48
    thanks
    MBC
    Sep 2009
    Iran
    66
    672
    1
    Re: Oil Type for HSN
    waiting for reply.
    11,025
    Bitzer document uses BS170 over range +7.5°C to -50°C
    Check docs here https://www.bitzer.de/gb/en/document...lng=en&lang=en
    495
    Hi if you use thin oil, it won't seal the screws properly to pump,
    Sep 2009
    Iran
    66
    672
    1
    pour point of BSE 170 is about - 28
    our SSD is - 45 and Evaporator working all the time
    ( O2) system and we do not have a defrost to return oil
    I looked the docs in Bitzer it wrote BSE 170
    I put mail to them Bitter but ......
    some thing is not right
    11,025
    If you do not trust the manufacturer then you wont trust anyone else.
    3,355
    Quote Originally Posted by GHAZ View Post
    I don’t really agree on that entirely.
    Oil selection usually to do with evaporating temperatures so not to thick to return.
    Sep 2009
    Iran
    66
    672
    1
    Dear Brian
    I trust them and read all of docs in there's sits
    But I put this question to them
    first they wrote oil should be BSE 170
    When I told them about pour point they mailed me BSE32
    I did a lots work with HSN and used BSE 170
    ( more than 60 cold rooms )
    But all of them was cold rooms ( -35 c) with defrost system
    this one has not defrost so I am not sure about type of oil
    for R 134A they wrote -25 c
    Sep 2003
    ISRAEL
    72
    4,248
    From My experience with Bitzer, Do not use any other oil.
    What is the compressor model?
    Sep 2009
    Iran
    66
    672
    1
    It is HSN 7471-75
    with ECO
    SST = -45
    SDT= 45
    R 404 A
    Before I used R 22 and oil were B100 it is mineral oil
    now I am going to use R 404 A
    Nov 2009
    france
    64
    223
    hi mbc,
    when you are reading the oil specifications, "In bitzer document for R=404A has BSE 170
    pour point of this oil =-28" >>> these -28 are for pure oil.
    in your system, refrigerant is mixed with oil and there is no problem in using BSE 170 at low temperatures.
    using iso32 oil you will get a high refrigerant concentration in oil at HP stage, low oil viscosity, and bad lubrification at bearings.