12kw 6000 liters Waterchiller pulldown time
customer has a small 12kw waterchiller they want to hook onto there 6000liter uninstalled plastic buffer tank, I dont have any flow rates but ive been trying to work out how long it would take to pull down from 20deg to 7degC tank only no other heatload - doesnt have to be accurate just a ruff idea but I am struggling to find a method, can anyboy help out or point me in the right direction
thanks
16-12-2018, 12:18 PM #2
Re: 12kw 6000 liters Waterchiller pulldown time
http://processheatingservices.com/wa...me-calculator/
or very roughly,
specific heat of water 4.18 KJ/kg k
1 Kg for 1 Litre of water
12 KJ/s cooling from chiller
13 degree temp change
Q=m x c x change in temp
Q=6000Kg x 4.18 KJ/Kg K x 13 degrees
Q=326040 KJ
Time taken with 12 Kw of cooling,
326040 KJ / 12 KJ/s / 60 seconds / 60 minutes = about 7.54 Hours
Lots of stuff not taken into account for though.Last edited by seanf; 16-12-2018 at 12:25 PM.
18-12-2018, 01:39 PM #3
Exactly what I was after, thanks very much!
18-12-2018, 02:50 PM #4
- Join Date
- Sep 2009
- Location
- Iran
- Age
- 66
- Posts
- 672
- Blog Entries
- 1
- Rep Power
- 19
Hi
the actual time is more than 7.54 h
you lose a lot of energy in plastic tank and piping and....
22-12-2018, 11:26 AM #5