    HI all,
    Got a call to look at a chiller last week. I haven't done any works on these Clivet chillers.
    Model # WSAT-XSC150F
    Customer told me that the previous maintenance company said a new EEV was needed.
    When I looked at the panel the following error codes are displayed
    U1/CMP2
    E128 Steeper Mot or Error Alarm
    U1/CMP2
    E103 Evaporator pressure probe
    Just wondering if I should change the EEV, the EEV module and the Evap probe?
    Thanks in advanve.
    Aug 2014
    70
    451
    Re: Clivet Chiller
    Change the evap probe first , if that doesn’t rectify it change the controller . You can get a manual controller handset to drive the stepper valve to see if it’s working most of the stepper valve manufacturers make these testers
    Mar 2009
    Ireland
    Re: Clivet Chiller
    Hey Glenn, solid advise.
    That's interesting on the manual controller.. need to look into that a but more..
    Nov 2005
    wales
    66
    15
    Re: Clivet Chiller
    Motor error may indicate a fault with the stepper motor coil. You could check for continuity between the motor poles. Should have 2 separate motor coils. You may have continuity between terminals 1&3, 2&4 for example.
    Mar 2009
    Ireland
    Re: Clivet Chiller
    Thank you Conrod,
    When I get back to site, likely 2019 now, i'll check this out.
    Mar 2009
    Ireland
    Re: Clivet Chiller
    Hi Guys, still haven’t got back to this chiller. Waiting on parts.
    But I have another error on an identical model as above.
    E126 SPI faulty alarm.
    Manual says E126 is MAX TS TEE peralarm.