    Sep 2005
    Granard, Ireland
    43
    Toshiba wall unit lost ability to heat
    Call out to Toshiba wall unit RAV-SM562KRT-E not heating.
    While cycling through the controller the heat symbol is missing and went into the system configuration menu, 0F-heat mode to select available but after saving this setting and going into the config. the controller shows 0001 unavailable
    The controller is RBC-AM31e
    I'm Stuck.. any advice
    FIXIT............first time every time
    Feb 2017
    77
    4
    Re: Toshiba wall unit lost ability to heat
    I dont know much about Toshiba units, but i do have a service manual for the above unit which i can send over to you in pdf if that would be any help?
    May 2006
    Hayling Island, UK
    55
    135
    Hi FIXIT,
    In my opinion there are three menus you need to check \ set up for all modes to be available.
    0d = 0000 (auto mode available)
    0F = 0000 (heat mode available)
    2d = 0015 (all modes available)
    GT Phelans in Bray should be able to help you - they're the Toshiba distributor for Eire
    Loops
    Sep 2005
    Granard, Ireland
    43
    Quote Originally Posted by Loops View Post
    Hi FIXIT,
    Loops
    Thanks folks
    It is a single system
    changed 0F to 0000 but it will not save that change.
    i will put it down to faulty indoor board.
    thanks.