    250Amp battery is 1Amp for 250 hours, 250 Amp for 1 hours or any combination in-between.
    A quick calculation with 3.5 kW load would require 1 kW input so your battery would last about 3 hours......
    If my maths is correct???
    Rob
    Mar 2013
    Germany
    5
    Re: 12 V DC Chiller Build
    Yes your right Maths is good.
    Rob what can i do.
    Spal Fan 8 A per Hour 2 Fans 16A per Hour what a Kompressor can i use Danfoss Bd250 12 V ?
    11,192
    Just need to ask - is the 250amps the battery capacity or its CCA cold cranking amperage (to start and engine)?
    According to the bd250 data sheet it should be around 7-8amps at -15°C, see page 22 -
    https://www.google.co.uk/url?sa=t&so...or81YW7-fYMqJe
    Mar 2013
    Germany
    5
    Hello Brian
    The Battery is 12V 200Ah Deep Cycle 800A/EN sorry fro my bad English.
    thanks for helping ,i see to page 22 max Ampere 4400 rpm 19,18Amps per hour
    20A+16A=36A (16 A 2 x Spal Fan)
    200A:36A=5,5 Hours of running ?
    11,192
    Agreed 19amps at maximum load.
    This load will reduce as the refrigerant load is pulled down towards your design temperature. Once at temperature the compressor operation will be further reduced as it comes under thermostat control.
    May 2012
    59
    1,537
    Quote Originally Posted by yilmaz22@gmx.de View Post
    Rob what can i do.
    Brian has a good point. as the load is achieved it will reduce the demand on the battery
    but it might only get you and extra 1/2 hour. Is it not as simple as getting another battery
    and doubling your supply?
    It will be hard to reduce power drawn due to the motors and other components design
    there is no easy way to reduce demand but you can double capacity of battery and that
    might be enough?
    Rob
    Mar 2013
    Germany
    5
    Thanks Guys
    i will inform you in some days i start build this unit .
    best thanks .
    i wait your Ideas
    5,733
    All well and good...but you should not drain a battery below 80% capacity.
    How is the battery recharged to continue the refrigeration cycle once down to temperature?
    Mar 2013
    Germany
    5
    Hello Frank
    the unit charged only with 240V,the Refrgeration runs 5-7 Hours from the battery(i Hope)
    and chardged after the work .
    best thanks Guys