    Dec 2005
    222
    Typical liquid temperature for txv selection
    It sounds simple enough however when using a TXV selection program there are tipping points that change the valve and orifice size if inputting different liquid temperatures.
    So;
    I sometimes don't have the info at the time of production therefore for a supermarket rack with a heat exchanger just before the valve I will generally use 70°f (21°C) as my liquid temp for valve selection. Any thoughts?
    Thanks, Ken
    3,362
    Re: Typical liquid temperature for txv selection
    Ken,
    I would have thought you would be indicating amount of liquid line subcooling to make selection. Delta p across valve important & would have thought 2-5 deg C subcooling at inlet of TX valve.
    Saturated condensing pressure of 25 deg C seems low, so you would look at possible minimum & maximum ambient temperatures to help selection as well.
    Liquid/suction line heat exchanger would not guarantee amount of subcooling though.
    Have you any feedback on previous selections?
    Dec 2005
    222
    Ranger 1, I've been selecting TXV's this way for many years without issue. However I'm working with a new installer who believes one of our selections should be larger which led to re-running the numbers research and this inquiry.
    Thanks for the feed back I'm sure more will be revealed.
    Ken
    11,025
    Sporlan documents 10-9 and 10-10 provide the correction factors to be applied to different liquid temperatures. Their baseline is 100°F.
    Download here http://sporlanonline.com/literature-...ansion-valves/
    3,362
    Ken,
    No worries, of course a number of ways to cross check things.
    After seeing Brians post I found this youtube link.
    We probably use Danfoss exclusively & they ask for different things than some others.
    https://www.youtube.com/watch?reload=9&v=LIFEQUUru4w
    Dec 2005
    222
    Thank you Brian_UK, I use the Sporlan Product Selection Program. Great tool.
    Ken