14-11-2018, 01:03 PM #1
Typical liquid temperature for txv selection
It sounds simple enough however when using a TXV selection program there are tipping points that change the valve and orifice size if inputting different liquid temperatures.
So;
I sometimes don't have the info at the time of production therefore for a supermarket rack with a heat exchanger just before the valve I will generally use 70°f (21°C) as my liquid temp for valve selection. Any thoughts?
Thanks, Ken
14-11-2018, 08:07 PM #2
Re: Typical liquid temperature for txv selection
Ken,
I would have thought you would be indicating amount of liquid line subcooling to make selection. Delta p across valve important & would have thought 2-5 deg C subcooling at inlet of TX valve.
Saturated condensing pressure of 25 deg C seems low, so you would look at possible minimum & maximum ambient temperatures to help selection as well.
Liquid/suction line heat exchanger would not guarantee amount of subcooling though.
Have you any feedback on previous selections?Last edited by RANGER1; 15-11-2018 at 06:55 AM.
15-11-2018, 12:18 PM #3
Ranger 1, I've been selecting TXV's this way for many years without issue. However I'm working with a new installer who believes one of our selections should be larger which led to re-running the numbers research and this inquiry.
Thanks for the feed back I'm sure more will be revealed.
Ken
15-11-2018, 03:57 PM #4
Sporlan documents 10-9 and 10-10 provide the correction factors to be applied to different liquid temperatures. Their baseline is 100°F.
Download here http://sporlanonline.com/literature-...ansion-valves/Brian - Newton Abbot, Devon, UK
15-11-2018, 08:02 PM #5
Ken,
No worries, of course a number of ways to cross check things.
After seeing Brians post I found this youtube link.
We probably use Danfoss exclusively & they ask for different things than some others.
https://www.youtube.com/watch?reload=9&v=LIFEQUUru4w
16-11-2018, 12:24 PM #6
Thank you Brian_UK, I use the Sporlan Product Selection Program. Great tool.
Ken