    Ammonia consumption



    Hi friends my plant is need refrigerant charge after few months without any likege it is normal ???



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Ammonia consumption

    No,
    There is a leak, you just didn't find it yet.

  3. #3
    Join Date
    Sep 2001
    Location
    London
    Age
    76
    Posts
    19
    Rep Power
    0

    Re: Ammonia consumption

    The last time I heard this an engineer was bleeding it off into water and selling it as a household cleaner!
    Len Fiddler

  4. #4
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Ammonia consumption

    Quote Originally Posted by manmohan View Post
    Hi friends my plant is need refrigerant charge after few months without any likege it is normal ???
    If you are sure no leakage it could be in a few places like condenser or in vessel on low side of system due to a solenoid leaking internally, suction trap has level it did not have before?
    Anyway, just guessing as we no nothing about your plant.

  5. #5
    Join Date
    Jul 2007
    Location
    Czech
    Age
    61
    Posts
    373
    Rep Power
    18

    Re: Ammonia consumption

    We know RANGER1, he does not have ammonia.

  6. #6
    Join Date
    Jul 2006
    Location
    USA
    Age
    73
    Posts
    867
    Rep Power
    26

    Re: Ammonia consumption

    Not usually a big problem with NH3 systems. I have solved may disappearing refrigerant issues by installing rupture discs under the relief valves. Thae tend to leak a little, then stop when the pressure falls, then start again when the pressure rises.

  7. #7
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: Ammonia consumption

    Quote Originally Posted by NH3LVR View Post
    Not usually a big problem with NH3 systems. I have solved may disappearing refrigerant issues by installing rupture discs under the relief valves. Thae tend to leak a little, then stop when the pressure falls, then start again when the pressure rises.
    A valid point based on Practical experience.

    Nice one!
    NH3LVR.
    Despite the High Cost of Living it still remains Popular!

  8. #8
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Ammonia consumption

    Quote Originally Posted by josef View Post
    We know RANGER1, he does not have ammonia.

    Josef,
    Not sure what you mean, did I miss something?

  9. #9
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,299
    Rep Power
    31

    Re: Ammonia consumption

    I believe NH3LVR is right ... also familiar to me ...

    safety valve discharge pipe usually venting refrigerants above roof into the air and minor leaks are hardly noticeable (old design school without ammonia sensor at the end of venting pipe)

    couple of months is quite a long time if system is relatively small and leak/s relatively big ...

    and safety valves check is usually once per year ...


    Just my opinion ...

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  10. #10
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Ammonia consumption

    Quote Originally Posted by Josip View Post
    I believe NH3LVR is right ... also familiar to me ...

    safety valve discharge pipe usually venting refrigerants above roof into the air and minor leaks are hardly noticeable (old design school without ammonia sensor at the end of venting pipe)

    couple of months is quite a long time if system is relatively small and leak/s relatively big ...

    and safety valves check is usually once per year ...


    Just my opinion ...

    Best regards, Josip

    Josip,
    Good to see you back, as has been awhile.
    Never heard of this scenario myself as a common thing.
    Pressures should never be higher than 10-15% of relief valve setting, that's where compressor trip points should be without exception.
    When valves are tested it should be checked for zero leakage at that pressure to check it's security after relief pressure set.
    Maybe poor quality reliefs?
    Rupture discs are good if multiple reliefs go into common header to see which one let go in event of release that should never happen.
    Also good for ***** or synthetic refrigerants to prevent loss of refrigerant.
    I also think your old school ammonia sensor on relief vent is best, also oil in "s" trap is good as well.

  11. #11
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,299
    Rep Power
    31

    Re: Ammonia consumption

    Hi, RANGER1 ... thanks ...
    been busy around house and family ... one son with his family moved into new house (rebuild old one) and there were never ending requests for help since spring time ... another son moved back to our house ... again repairs, improvements, paintings ... 12 hours a day shift ... and still not finished, but winter is coming and some works we have to postpone until next year spring or summer ....


    Quote Originally Posted by RANGER1 View Post
    Josip,
    Good to see you back, as has been awhile.
    Never heard of this scenario myself as a common thing.
    Pressures should never be higher than 10-15% of relief valve setting, that's where compressor trip points should be without exception.
    When valves are tested it should be checked for zero leakage at that pressure to check it's security after relief pressure set.
    Maybe poor quality reliefs?
    Rupture discs are good if multiple reliefs go into common header to see which one let go in event of release that should never happen.
    Also good for ***** or synthetic refrigerants to prevent loss of refrigerant.
    I also think your old school ammonia sensor on relief vent is best, also oil in "s" trap is good as well.

    It is not a common thing ... more exception ... can be effect due to lack of good relief valves pressure test .... poor quality reliefs ... for some reason running plant at high discharge pressure ... some reliefs are equipped with handle for manual operation for check and maybe not close tight after check or just be opened by accident during installation without note to supervisor (to retest relief) ... new plant ... maybe young operators without a lot of experience ... etc .. kind of Murphy's law ...

    ... as I remember happened to me only on two plants (each with only one relief passing, but all were connected to common header going over roof and not quite good for access) so it is not so common but can happen ...

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •