    Jun 2014
    india
    30
    Ammonia consumption
    Hi friends my plant is need refrigerant charge after few months without any likege it is normal ???
    Sep 2003
    ISRAEL
    72
    4,248
    Re: Ammonia consumption
    No,
    There is a leak, you just didn't find it yet.
    Sep 2001
    London
    The last time I heard this an engineer was bleeding it off into water and selling it as a household cleaner!
    Len Fiddler
    3,359
    Quote Originally Posted by manmohan View Post
    If you are sure no leakage it could be in a few places like condenser or in vessel on low side of system due to a solenoid leaking internally, suction trap has level it did not have before?
    Anyway, just guessing as we no nothing about your plant.
    Jul 2007
    Czech
    61
    373
    We know RANGER1, he does not have ammonia.
    Jul 2006
    865
    Not usually a big problem with NH3 systems. I have solved may disappearing refrigerant issues by installing rupture discs under the relief valves. Thae tend to leak a little, then stop when the pressure falls, then start again when the pressure rises.
    4,700
    Quote Originally Posted by NH3LVR View Post
    A valid point based on Practical experience.
    Nice one!
    NH3LVR.
    3,359
    Quote Originally Posted by josef View Post
    Josef,
    Not sure what you mean, did I miss something?
    Croatia
    68
    2,261
    I believe NH3LVR is right ... also familiar to me ...
    safety valve discharge pipe usually venting refrigerants above roof into the air and minor leaks are hardly noticeable (old design school without ammonia sensor at the end of venting pipe)
    couple of months is quite a long time if system is relatively small and leak/s relatively big ...
    and safety valves check is usually once per year ...
    Just my opinion ...
    Best regards, Josip
    3,359
    Just my opinion ...
    Best regards, Josip
    Josip,
    Good to see you back, as has been awhile.
    Never heard of this scenario myself as a common thing.
    Pressures should never be higher than 10-15% of relief valve setting, that's where compressor trip points should be without exception.
    When valves are tested it should be checked for zero leakage at that pressure to check it's security after relief pressure set.
    Maybe poor quality reliefs?
    Rupture discs are good if multiple reliefs go into common header to see which one let go in event of release that should never happen.
    Also good for ***** or synthetic refrigerants to prevent loss of refrigerant.
    I also think your old school ammonia sensor on relief vent is best, also oil in "s" trap is good as well.
    Croatia
    68
    2,261
    Hi, RANGER1 ... thanks ...
    been busy around house and family ... one son with his family moved into new house (rebuild old one) and there were never ending requests for help since spring time ... another son moved back to our house ... again repairs, improvements, paintings ... 12 hours a day shift ... and still not finished, but winter is coming and some works we have to postpone until next year spring or summer ....
    Josip,
    It is not a common thing ... more exception ... can be effect due to lack of good relief valves pressure test .... poor quality reliefs ... for some reason running plant at high discharge pressure ... some reliefs are equipped with handle for manual operation for check and maybe not close tight after check or just be opened by accident during installation without note to supervisor (to retest relief) ... new plant ... maybe young operators without a lot of experience ... etc .. kind of Murphy's law ...
    ... as I remember happened to me only on two plants (each with only one relief passing, but all were connected to common header going over roof and not quite good for access) so it is not so common but can happen ...
    Best regards, Josip