    Mar 2018
    Canada
    5
    Changing refrigerants
    Purchased an older walk in cooler that was charged with r12 want to change to 134a what kind of oil do I need to use has aklyate synthetic in it now or would there be a better choice of refrigerants
    Sep 2003
    ISRAEL
    72
    4,266
    Re: Changing refrigerants
    You need to emty the compressor, charge with POE, the oil viscosity depends on evaporating temp,
    Run some refrigerant oil cleaner through the pipe work, pushing it with OFN, replace the TXV to 134 one, new drier, good vacuum, charge and run the unit.
    Mar 2018
    Canada
    5
    Thanks will try that
    Mar 2018
    Canada
    5
    Would there be a better choice of refrigerant other than 134a
    Mar 2012
    denmark
    4
    Check out Lindes "Retrofit Guide", they suggest a few alternatives like R423A, R426A, R437A depending on application, and suggests oil changes.
    Remember to renew gaskets and check the superheat settings