    Refrigerant Phase is liquid receiver - when shut off



    What would be the refrigerant phase when the system is off? I have seen the pressure on both sides equalizes after sometime (after shut off) at around 150psig. At this point, will refrigerant stay as liquid in the receiver? Wouldn't it be spread through out the system? If Yes, wouldn't it defeat the purpose of receiver at the first place?



  2. #2
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36

    Re: Refrigerant Phase is liquid receiver - when shut off

    .

    The refrigerant would be saturated.

    Just the same as if it was in a cylinder and yes eventually the
    refrigerant would equalise throughout the whole system. If there
    are solenoid valves fitted then the equalisation would be slower
    but it would equalise never the less.