    Re: Refrigerant Phase is liquid receiver - when shut off

    .

    The refrigerant would be saturated.

    Just the same as if it was in a cylinder and yes eventually the
    refrigerant would equalise throughout the whole system. If there
    are solenoid valves fitted then the equalisation would be slower
    but it would equalise never the less.

    Rob

    .
    Last edited by Rob White; 19-08-2018 at 09:50 AM.
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..