    Question Eliwell EXTK manual
    Hello All,
    wondering if anyone has any manuals or info on this controller please chiller.jpg
    All it says EXTK on the front and the closest i can find online is a Eliwell XT PRO, if anyone has a manual for it or can help me with fault code that appears on compressor 2 (which we have currently taken off the system)
    The fault code is showing OR Sensor Fault Compressor 2, but having no info on the system what so ever makes it difficult knowing what OR sensor is, i did wonder if it was Oil Regulator? but then why would it only start having this fault as of friday when we disconnected the comp 3 weeks ago?
    Thanks all
  2. #2
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,090
    Rep Power
    33
    Re: Eliwell EXTK manual
    I googled it and there seems to be downloads available
  3. #3
    Join Date
    Feb 2017
    Location
    UK
    Posts
    112
    Rep Power
    9
    Quote Originally Posted by cadwaladr View Post
    really? i'll have another look then, when i googled it when i was on site i couldnt find anything about it
  4. #4
    Join Date
    Feb 2017
    Location
    UK
    Posts
    112
    Rep Power
    9
    Got one, thank you, for some reason i couldnt fine one earlier but i have now got one
  5. #5
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,090
    Rep Power
    33
    Well done,another success story love it when a plan comes together
  6. #6
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60
    Bear in mind that the controller has been programmed by the chiller manufacturer and you need the print out of all of the parameters.
    The actual front end display is as thick as two planks without the parameter schedule.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015
  7. #7
    Join Date
    Feb 2017
    Location
    UK
    Posts
    112
    Rep Power
    9
    Quote Originally Posted by Brian_UK View Post
    Thanks for your help Brian, yes i spoke with the manufacturer as well and sorted it.
    Thanks for everyones help