    Unhappy Carrier 30HXC200--0024-AEE



    Hi,

    I have some troubles with 2 chillers both Carrier 30HXC200--0024-AEE with Carrier Pro-Dialog Plus black display from year 2000.
    The software is a version 3 or 4.
    We are getting error 113 and 213 on both chillers, according to the manual a have is it relating to the setpunkt reset but the errors are coming even with wires disconnectet and running the chiller in local or remote.
    It is only a warning the chiller is running with the warning.
    What is causing this?
    Last edited by oz4rg; 07-08-2018 at 08:43 AM.



  2. #2
    Join Date
    Sep 2010
    Location
    Kazakhstan
    Age
    45
    Posts
    36
    Rep Power
    0

    Re: Carrier 30HXC200--0024-AEE

    Can you show this manual with 113 and 213 alrm codes? I found some for black HXC screw prodialog. And this alarms are Current phase reversal. Grey prodialog shows Star-delta start-up alarm.
    http://eto.carrier.com/lit.asp

  3. #3
    Join Date
    Jun 2012
    Location
    Denmark
    Posts
    6
    Rep Power
    0

    Re: Carrier 30HXC200--0024-AEE

    You can see error X13 in this manual: 30HXCPhaseII

  4. #4
    Join Date
    Jun 2006
    Location
    South Coast
    Posts
    269
    Rep Power
    18

    Re: Carrier 30HXC200--0024-AEE

    Can't see that alarm, there is no setpoint reset alarm. The HXC phase 2 manual on the Carrier website as previously stated shows phase reversal.
    Gibbo

  5. #5
    Join Date
    Jun 2012
    Location
    Denmark
    Posts
    6
    Rep Power
    0

    Re: Carrier 30HXC200--0024-AEE

    Sorry you are right.
    But the chillers are running...
    They wouldnt be running with phase reversal...

  6. #6
    Join Date
    Sep 2010
    Location
    Kazakhstan
    Age
    45
    Posts
    36
    Rep Power
    0

    Re: Carrier 30HXC200--0024-AEE

    Compressor wouldnt be running but not the chiller. For example if 113 alarm is - comp A1 shut down.
    Last edited by Sserrviceman; 10-08-2018 at 02:35 PM.

  7. #7
    Join Date
    Jun 2006
    Location
    South Coast
    Posts
    269
    Rep Power
    18

    Re: Carrier 30HXC200--0024-AEE

    Maybe you were looking at alarm history and not current alarms.

  8. #8
    Join Date
    Jun 2012
    Location
    Denmark
    Posts
    6
    Rep Power
    0

    Re: Carrier 30HXC200--0024-AEE

    Marriot.jpg
    Please see this Picture:

  9. #9
    Join Date
    Jun 2012
    Location
    Denmark
    Posts
    6
    Rep Power
    0

    Re: Carrier 30HXC200--0024-AEE

    And this off the other chiller:
    Marriot1.jpg

  10. #10
    Join Date
    Sep 2010
    Location
    Kazakhstan
    Age
    45
    Posts
    36
    Rep Power
    0

    Re: Carrier 30HXC200--0024-AEE

    Did you try to reset the alarm?

  11. #11
    Join Date
    Jun 2012
    Location
    Denmark
    Posts
    6
    Rep Power
    0

    Re: Carrier 30HXC200--0024-AEE

    Yes, I can reset the alarms with out trouble, but the alarms are comming again about 5-30 min.
    Both chillers are running with the failures and with both Circuits ( 2+1 screws on both chillers).