    Unhappy Carrier 30HXC200--0024-AEE



    Hi,

    I have some troubles with 2 chillers both Carrier 30HXC200--0024-AEE with Carrier Pro-Dialog Plus black display from year 2000.
    The software is a version 3 or 4.
    We are getting error 113 and 213 on both chillers, according to the manual a have is it relating to the setpunkt reset but the errors are coming even with wires disconnectet and running the chiller in local or remote.
    It is only a warning the chiller is running with the warning.
    What is causing this?
    Last edited by oz4rg; 07-08-2018 at 08:43 AM.



  2. #2
    Join Date
    Sep 2010
    Location
    Kazakhstan
    Age
    51
    Posts
    36
    Rep Power
    0

    Re: Carrier 30HXC200--0024-AEE

    Can you show this manual with 113 and 213 alrm codes? I found some for black HXC screw prodialog. And this alarms are Current phase reversal. Grey prodialog shows Star-delta start-up alarm.
    http://eto.carrier.com/lit.asp

  3. #3
    Join Date
    Jun 2012
    Location
    Denmark
    Posts
    7
    Rep Power
    0

    Re: Carrier 30HXC200--0024-AEE

    You can see error X13 in this manual: 30HXCPhaseII

  4. #4
    Join Date
    Jun 2006
    Location
    South Coast
    Posts
    278
    Rep Power
    23

    Re: Carrier 30HXC200--0024-AEE

    Can't see that alarm, there is no setpoint reset alarm. The HXC phase 2 manual on the Carrier website as previously stated shows phase reversal.
    Gibbo

  5. #5
    Join Date
    Jun 2012
    Location
    Denmark
    Posts
    7
    Rep Power
    0

    Re: Carrier 30HXC200--0024-AEE

    Sorry you are right.
    But the chillers are running...
    They wouldnt be running with phase reversal...

  6. #6
    Join Date
    Sep 2010
    Location
    Kazakhstan
    Age
    51
    Posts
    36
    Rep Power
    0

    Re: Carrier 30HXC200--0024-AEE

    Compressor wouldnt be running but not the chiller. For example if 113 alarm is - comp A1 shut down.
    Last edited by Sserrviceman; 10-08-2018 at 02:35 PM.

  7. #7
    Join Date
    Jun 2006
    Location
    South Coast
    Posts
    278
    Rep Power
    23

    Re: Carrier 30HXC200--0024-AEE

    Maybe you were looking at alarm history and not current alarms.

  8. #8
    Join Date
    Jun 2012
    Location
    Denmark
    Posts
    7
    Rep Power
    0

    Re: Carrier 30HXC200--0024-AEE

    Marriot.jpg
    Please see this Picture:

  9. #9
    Join Date
    Jun 2012
    Location
    Denmark
    Posts
    7
    Rep Power
    0

    Re: Carrier 30HXC200--0024-AEE

    And this off the other chiller:
    Marriot1.jpg

  10. #10
    Join Date
    Sep 2010
    Location
    Kazakhstan
    Age
    51
    Posts
    36
    Rep Power
    0

    Re: Carrier 30HXC200--0024-AEE

    Did you try to reset the alarm?

  11. #11
    Join Date
    Jun 2012
    Location
    Denmark
    Posts
    7
    Rep Power
    0

    Re: Carrier 30HXC200--0024-AEE

    Yes, I can reset the alarms with out trouble, but the alarms are comming again about 5-30 min.
    Both chillers are running with the failures and with both Circuits ( 2+1 screws on both chillers).

  12. #12
    Join Date
    Jan 2011
    Location
    London
    Age
    38
    Posts
    43
    Rep Power
    0

    Re: Carrier 30HXC200--0024-AEE

    Hi Oz4rg
    the alarm 113=compressor A1 and 213=A2 Phase reversal fault
    with this fault it will prevent all compressors on circuit A from running but circuit b should be fully operational
    now what you need to look for is a klixson within the starter panel this is a common issue on the phase two
    and will generate a phase reversal alarm dont know why but it does
    also if the panel klixson is ok then just link out the phase reversal relay once you prove that the relay is faulty quote to replace but dont leave the relay linked out these issues are common on carrier chillers