    sight glass installation



    Hi guys
    I wonder to know if it is wrong to use smaller size of sight glass on a larger liquid line like bypass pipe? i mean to install a parallel smaller pipe (flare connection) with the main liquid line and a sight glass on it.
    the picture below:
    Thanks
    photo_۲۰۱۸-۰۴-۲۱_۱۱-۵۱-&.jpg
    Last edited by NaderAttar; 30-07-2018 at 12:08 PM.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: sight glass installation

    That installation is basically correct, the sightglass should be facing upwards.

    Download Sporlan installation document SD 21 from here - https://bit.ly/2Lz2G8s
    Brian - Newton Abbot, Devon, UK