Thread: Climaveneta alarm131
24-07-2018, 01:24 PM #1
Dear,I have climaveneta chiller,and i have alarm 131.
What is the problem?
24-07-2018, 02:00 PM #2
Re: Climaveneta alarm131
Compressor no. 1 overheated or other problem.
https://www.google.co.uk/url?sa=t&so...QImOIUmazLPQsJBrian - Newton Abbot, Devon, UK
24-07-2018, 02:06 PM #3
Yes ,i know what is this alarm ,but what can i do now to solve the problem?
24-07-2018, 06:36 PM #4
Very hard to see from here what may be wrong.
Only guessing at what might be running at the time so I'm going pick a faulty fan motor or maybe a refrigerant leak.
I would suggest that you contact a refrigeration company to investigate the problem and advise on remedial action.Brian - Newton Abbot, Devon, UK
19-08-2018, 02:50 PM #5
On circuit 1 have 6 fan motors command with 3 relay ,i change to operate relay 1 in same time with relay 2 and relay 3 to operate with signal from relay 2.Now is good but ones in the day we have again alarm 131.
30-07-2018, 09:06 AM #6
I check motor temperature during work,it is over 100 degree.We add ref 134A but again we have alarm 131.
13-08-2018, 02:50 PM #7
I change the fer.134A and add new with factory value 60kg for this circuit ,and also we change the filters ,but after this service again we have same alarm 131 .