    Hello everybody!

    I have a problem - the burning of the windings of two electric motors.
    There is a rubber stopper on the motor housing.
    The question is - should it be removed or not?
    The chiller works only in the summer. A maximum of three months a year.20180718_083931.jpg20180718_091755.jpg20180718_092837.jpg



  2. #2
    Join Date
    Feb 2011
    Location
    Russia
    Posts
    26
    Rep Power
    0

    Re: Moisture inside the motor housing. Manufacturer Leroy Somer

    first photo - the lower part of the motor.
    second photo - bottom cover from the inside.
    The third photo shows the top cover on the outside.
    This is the electric motor of the condenser fan. Installed vertically.
    Last edited by NEugeny; 23-07-2018 at 11:01 AM.

  3. #3
    Join Date
    Dec 2010
    Location
    Greece
    Posts
    181
    Rep Power
    14

    Re: Moisture inside the motor housing. Manufacturer Leroy Somer

    you should seek information from manufacture company.
    look for a manual with regard to this make of fan.
    my opinion is that you should remove this cap from the fan.then it would be possible for excessive moisture to be drained off through this hole.

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Moisture inside the motor housing. Manufacturer Leroy Somer

    What are the off season temperatures/conditions.

    I would suggest removing the motors at the end of the cooling season and put them into dry storage prior to refitting at the next season.

    If not then perhaps fit electric heaters to keep them dry.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,471
    Rep Power
    41

    Re: Moisture inside the motor housing. Manufacturer Leroy Somer

    If the rubber is on the bottom of the motor when installed then remove it. Any condenser fan motor that is off for long periods will have issues. Can you arrange for chiller to cycle once a week for an hour to allow motors to run?
    Mostly found in the southern part of this green and pleasant land.

  6. #6
    Join Date
    Feb 2011
    Location
    Russia
    Posts
    26
    Rep Power
    0

    Re: Moisture inside the motor housing. Manufacturer Leroy Somer

    The rubber stopper installed on the top cover. This hole is closed from above by the impeller, and to access it, it is necessary to remove the protective grille and impeller.
    There are also no seals between the motor casing and the top and bottom covers.
    The second chiller, which operates all year round, has no problems with the electric motors.
    This chiller (C .... er) does not have a winter option, and the fans operate in automatic mode.
    It will be very problematic to run the fans manually, while removing snow and ice from the impellers.
    The lower part of the motor has seals, and there are no drainage or ventilation openings.

  7. #7
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Moisture inside the motor housing. Manufacturer Leroy Somer

    Had a similar problem, is it a carrier chiller?

    Replaced them with ebm fans. no more problems. you should expect bearing failure. not a good motor.

  8. #8
    Join Date
    Feb 2011
    Location
    Russia
    Posts
    26
    Rep Power
    0

    Re: Moisture inside the motor housing. Manufacturer Leroy Somer

    Quote Originally Posted by chemi-cool View Post
    Had a similar problem, is it a carrier chiller?

    Replaced them with ebm fans. no more problems. you should expect bearing failure. not a good motor.
    1. Yes, bingo!!!
    2. Exactly, the upper bearing has increased noise, compared to the lower one. The motor coast is still normal, the noise is heard only when the rotor rotates, in disassembled condition.

  9. #9
    Join Date
    Feb 2011
    Location
    Russia
    Posts
    26
    Rep Power
    0

    Re: Moisture inside the motor housing. Manufacturer Leroy Somer

    Quote Originally Posted by Brian_UK View Post
    What are the off season temperatures/conditions.
    I would suggest removing the motors at the end of the cooling season and put them into dry storage prior to refitting at the next season.
    If not then perhaps fit electric heaters to keep them dry.
    1. Temperature conditions: summer - to +35°C, winter - to minus 49°C.
    2. Sense in the dismantling of electric motors, I do not see, as water gets inside during the warm period of the year with daily fluctuations in temperature. Number of motors - 21 pcs.
    3. The thought is good, but one must think carefully about the ways in which this can be done.

  10. #10
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Moisture inside the motor housing. Manufacturer Leroy Somer

    Quote Originally Posted by NEugeny View Post
    1. Yes, bingo!!!
    2. Exactly, the upper bearing has increased noise, compared to the lower one. The motor coast is still normal, the noise is heard only when the rotor rotates, in disassembled condition.
    I replace them with Ziel Abeg. 900 rpm 650 mm [if I remember right]. Electric cabel is long enough .
    Carrier refused to sell only the motor, only a kit with motor and their blades.

  11. #11
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: Moisture inside the motor housing. Manufacturer Leroy Somer

    very helpful Chemi.
    Rep point sent!
    Grizzly
    Despite the High Cost of Living it still remains Popular!

  12. #12
    Join Date
    Feb 2011
    Location
    Russia
    Posts
    26
    Rep Power
    0

    Re: Moisture inside the motor housing. Manufacturer Leroy Somer

    Quote Originally Posted by chemi-cool View Post
    I replace them with Ziel Abeg. 900 rpm 650 mm [if I remember right]. Electric cabel is long enough .
    Carrier refused to sell only the motor, only a kit with motor and their blades.
    Many thanks for the help. I'll try to find a fan suitable for the fixing and diameter of the impeller.