22-07-2018, 08:48 AM #1
Re: Digital scroll chiller
Which controller are you using for the EEV? Is it the EC3 D73 by any chance? If so, then when the compressors cycle off, does the enable (0-10v/4-20ma) also drop out?
Also what do you have the minimum valve opening position at upon startup set to?
Have you got a controller to be able to go in and check the settings that theThe difference between genius and stupidity is that genius has its limits.
Marc
-
22-07-2018, 12:33 PM #2
Re: Digital scroll chiller
No, itīs an Eliwell XVD, but I also have a Dixell XEV22 to work with if that would mean a solution.
Actually the valve controller has no way of realizing the compressor is not cycling in this setup, the digital input is enabled throughout the whole cycle. I have not found any parameters (but maybe there is a way I can not find so far) to allow me to keep the valve open while on the OFF cycle.
I am using the suggested 85 % as the opening position valve, but problems are not happening during startup, actually itīs sort of a stabilized system issue.