    Rxyscq5tmv1b gas charge



    Hi folks .
    just wanted some advice for a system I am working on.
    the factory 410a charge. Is3.7 kg
    I reclaimed 4.73kg my pipe work is as follows 5/8 3/8 outdoor to refnets is19 meters
    and to the units from the refnets is 9meters
    is this charge correct?
    The problem in the winter was it stayed in defrost for quite some time.
    any ideas are welcome.
    as its baking hot. At the moment I would like to get this going again tomorrow. Afterto days. Pressure test of the pipe work .

    Cheers in advance



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Rxyscq5tmv1b gas charge

    Don't know how many units you have connected but the additional charge per metre should be 0.059kg for the liquid line.