    Mitsubishi Electric - PKA-RP50HAL

    Afternoon,

    We have the above unit in our office at work, I notice that there is a blue thermister sensor in the air outlet. Possibly the evaporator sensor. Is this in the correct place or is there a place it should be? See attached picture...

    IMG_20180703_141447158.jpg

    Just wondering the logic for putting it here, as usually they are mounted on the pipework in a little slot the same as the pipe temp sensor?

    Is it better for it to be in this position to read the air off?

    According to https://planetaklimata.com.ua/instr/...Manual_Eng.pdf there is just the 3 sensors, evap, pipe & return air sensor.

    Unit is working properly but wondered if this is in the right place. The air off is nice and cold.

    Thank you.
    Richard.
    Last edited by back2space; 03-07-2018 at 02:17 PM.