    Oct 2009
    Norway
    Water pump capacity
    If i have a closed water circuit in a Building with 5 floors.
    Would it require the same water pump capacity if the water pump was placed on the 5. floor Vs 1. floor?
    70
    10,624
    52
    Re: Water pump capacity
    Shouldn't make any difference.
    The pressurisation unit pressure settings will be dependant on its location.
    Sep 2008
    Canada
    775
    12
    You need pump with greater head.
    70
    10,624
    52
    Please explain.
    Sep 2008
    Canada
    775
    12
    Every centrifugal pump has nominal head and capacity. To provide required capacity for 5th floor, pump should have greater head. Usually, head can be increased by choosing two stages pump. Assume that the lift is 15 meters. It means that nominal head of the pump should be 1.5 bars greater than nominal head of the pump for the first floor.
    Aug 2008
    49
    256
    But what about the weight/pressure of the returning water? I could be wrong, but what you're describing is pumping water to height with no return path?
    Jul 2006
    68
    734
    It is true that the return will negate the head required to reach a height in a system.
    However you have to get liquid up to a higher point before this works. (Over the hump, so to speak)
    And should you have air or the system is stopped you may not be able to get it going again.
    Sep 2008
    Canada
    775
    12
    You are right. I mentioned about open loop system. For closed loop I would be concerned about cavitation on suction side. Pump located on first floor will not have cavitation.