Thread: Water pump capacity
-
21-06-2018, 05:20 PM #1
Water pump capacity
If i have a closed water circuit in a Building with 5 floors.
Would it require the same water pump capacity if the water pump was placed on the 5. floor Vs 1. floor?
-
21-06-2018, 08:09 PM #2
Re: Water pump capacity
Shouldn't make any difference.
The pressurisation unit pressure settings will be dependant on its location.Brian - Newton Abbot, Devon, UK
Retired March 2015
-
26-06-2018, 07:12 PM #3
Re: Water pump capacity
You need pump with greater head.
-
26-06-2018, 10:15 PM #4
-
27-06-2018, 12:52 AM #5
Re: Water pump capacity
Every centrifugal pump has nominal head and capacity. To provide required capacity for 5th floor, pump should have greater head. Usually, head can be increased by choosing two stages pump. Assume that the lift is 15 meters. It means that nominal head of the pump should be 1.5 bars greater than nominal head of the pump for the first floor.
-
27-06-2018, 02:03 AM #6
-
27-06-2018, 05:13 PM #7
Re: Water pump capacity
It is true that the return will negate the head required to reach a height in a system.
However you have to get liquid up to a higher point before this works. (Over the hump, so to speak)
And should you have air or the system is stopped you may not be able to get it going again.
-
27-06-2018, 05:37 PM #8
Re: Water pump capacity
You are right. I mentioned about open loop system. For closed loop I would be concerned about cavitation on suction side. Pump located on first floor will not have cavitation.