    Thumbs down Eco triple fan freezer evaporator fan wiring



    Worked on one of these evaporators today one of the fans had siezed ,replaced the fan motor and it did not run although the other two did checked for power no voltage traced it to what i can only call a stupid connection block located behind the fan,so one cable comes out of the junction box then hidden in the path to motors is this connection block yes its oem,I have seen some crazy ways to wire stuff but this is out of the idiots manual.



  2. #2
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,471
    Rep Power
    41

    Re: Eco triple fan freezer evaporator fan wiring

    Yep, absolute balls of an evaporator, fitted one, never again!
    Mostly found in the southern part of this green and pleasant land.

  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Eco triple fan freezer evaporator fan wiring

    What fan make and model?
    EBM has wierd connections.

  4. #4
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,097
    Rep Power
    33

    Re: Eco triple fan freezer evaporator fan wiring

    No problem with the fan,it was they way eco wire the supply they should have wired each motor to the junction box instead of one feed out of the box and crazy junctions enroute to the motors,ok it saves about .5 of a metre of cable but mental