    Aug 2016
    32
    95
    8
    How toxic are refrigerants?
    I know that Class A refrigerants are supposedly non toxic. But how toxic are they? Are refrigerants any more toxic than any other inert gas, such as helium or nitrogen? Also, what would happen if an AC system blew the evaporator coil and suddenly released all the refrigerant into the house? Would there be any adverse health effects?
    11,025
    Re: How toxic are refrigerants?
    Assume any gas that dilutes normal air oxygen levels as a danger.
    There are calculations to be performed to ensure that the safe gas charge/room size concentration is in range.
    Check the MSDS for the refrigerant you are concerned about regarding toxicity.
    Aug 2016
    32
    95
    8
    Thank you. Just curious- Is refrigerant any more likely to be dangerous than another inert gas, like nitrogen?
    Sep 2003
    ISRAEL
    72
    4,248
    When oxygen in the air you breathing goes below 18%, you start to suffocate.
    The cause is irrelevant.
    It can be refrigerant or Nitrogen or any other gas.
    4,697
    Hi Cool Guy.
    I can say that refrigerants are potentially more Dangerous than Nitrogen.
    But you need to put it all into perspective.
    How many people do you know that have been injured / harmed by a contained refrigerant in a working A/C system.
    I doubt any, I as a refrigeration engineer of many years know of some who have had a scare!
    When working on a system.
    You can always make a case for something being dangerous.
    The less product knowledge you have the easier it is.
    However do you apply these same rules to the other energy sources that may exist in a given area.
    IE. Electricity, Flammable Gasses such as. Natural or Liquefied Petroleum Gas.
    Refrigerant volumes and types are carefully considered in an A/C install and the volumes that could be released.
    I must admit I am trying to work out what the purpose of your question is?
    Refrigerants and Nitrogen both replace air and therefore can cause suffocation.
    Both could be lethal if a sufficient amount is inhaled.
    But as to which is deemed more toxic is irrelevant really.
    What circumstances are you thinking of that caused you to ask?
    We don't class water as toxic but it kills!" (In the wrong Circumstances.)
    Aug 2016
    32
    95
    8
    Quote Originally Posted by chemi-cool View Post
    So the refrigerant itself isn't harmful, but the lack of oxygen is? So in that case, what would happen if a person was breathing 80% refrigerant and 20% oxygen?
    May 2012
    59
    1,528
    Refrigerants by their nature are not inert.
    Inert means it won't react with anything, most refrigerants
    will react. How they react does depend on the individual refrigerant.
    Most, if not all will only react under excessive temperature and the
    refrigerant will thermally decompose.
    Some of the more common refrigerants will cause a person to suffer
    irregular heartbeats and some can cause the central nervous system
    to be affected and that can cause confusion and loss of concentration.
    None of the common refrigerants are classed as toxic because they
    do not poison or have any detrimental long term effects on people
    under normal conditions.
    Rob
    May 2012
    59
    1,528
    Quote Originally Posted by coolguy4 View Post
    If you have access to 6% oxygen technically you can survive but the
    refrigerant in such a large concentration would affect you in the way
    I stated above.
    Irregular heartbeats and CNS effect.
    Rob
    3,358
    Maybe this will help understand effects.
    Like anything MSDS should be read & understood before using it in the perfect world.
    https://www.healthline.com/health/re...ning#treatment
    http://www.afrox.co.za/internet.glob...7719.pdf?v=2.0