    Hi, anyone now if it possible to calibrate the reading of the temperature probes and the transducer on this control?
    Thanks
    Attached Images Attached Images



  2. #2
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,471
    Rep Power
    41

    Re: Help trane adaptive control

    I think you need Trane tracer software to do anything on these chillers, what problems are you having with it?
    Mostly found in the southern part of this green and pleasant land.

  3. #3
    Join Date
    May 2017
    Location
    portugal
    Age
    44
    Posts
    5
    Rep Power
    0

    Re: Help trane adaptive control

    Hi Al, thanks for the replay.
    In having a alarm low temperature rfgt, and the probe next to exp valve is reading low then the real temperature. The refrigerant is all inside.

  4. #4
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,471
    Rep Power
    41

    Re: Help trane adaptive control

    Could it just be a faulty probe?