    Critical Path for External Static Pressure Calculations



    Hello,

    For ESP calculations, generally I've seen Engineers selecting the longest duct run, which has most pressure drop. It is said, this selection is enough to over come pressure drop in other ducts.

    I have my doubts here. Lets consider the longest duct run has 500Pa ESP with its sound attenuators, dampers all misc accessories. Assume there is a branch duct connected to it having a pressure drop of 200Pa.
    Will 500Pa ESP be enough, or should 700Pa be considered?

    If its just 500Pa, I don't understand the logic of how this air can over come this additional 200Pa, when it has already burned out its energy to overcome 500Pa static??



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Critical Path for External Static Pressure Calculations

    Can I recommend the grandfather of fan/duct design.

    Woods Practical Guide to Fan Engineering.


    https://bit.ly/2rEnhLZ
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Critical Path for External Static Pressure Calculations

    The longest duct run is not necessarily the most resistive to airflow.
    what we generally calculate is the index circuit. This is the route that the working fluid has to travel against the greatest resistance in the system.
    If the fan or pump can overcome this resistance then it quite easily overcome the resistance in any lesser resistive branch ducts or pipe runs

  4. #4
    Join Date
    May 2011
    Location
    India
    Age
    38
    Posts
    106
    Rep Power
    13

    Re: Critical Path for External Static Pressure Calculations

    Quote Originally Posted by Brian_UK View Post
    Can I recommend the grandfather of fan/duct design.

    Woods Practical Guide to Fan Engineering.


    https://bit.ly/2rEnhLZ
    Thanks man!