    clivet chiller



    2x clivet wasat-22140 chillers on r407c have phase monitor alarm. alarm will clear but then come
    back, chillers will not run. trend controller is showing the chillers enabled set point is 15c water inlet temp is 27c ambient temp today was 24c.
    Checked 3-phase supply which seems balanced, so does anyone know where to find the monitor
    and how to check it. Also noticed top pressurisation set leaking water but this is another fault.
    Asked the customer if any phase reversal has taken place,but they are not aware of anything.
    The only other work carried out recently is some heating pumps have been changed in a boiler house,but i cannot see this is relevant.



  2. #2
    Join Date
    Oct 2009
    Location
    england
    Age
    77
    Posts
    243
    Rep Power
    19

    Re: clivet chiller

    Is there a carel RSF relay or have the sparkles been messing about in the H&V panel