    Dear Friends,
    I have a question.

    Regarding compressors in parallel systems, Some sources such a ASHRAE emphasize on this matter that beside of suction and discharge pipes we must join oil line + gas equalizer line such as photo at below :


    2.jpg

    Some companies such as LG and …. use this rule when they want to parallel compressors.

    But some other sources such as EMERSON (COPELAND) on SCROLL compressors and CARLYLE (CARRIER) on semi-hermetic compressors just join suction/discharge/oil of crankcase (no need gas equalizer line). See example below :

    Carrier 1.jpg

    Which one say true ??

    Sincerely yours.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Parallel compressors

    .....Both, capacity controls, oil level controls all can have a bearing on the piping required.