    Bypass desuper heater with Sporlan ORI



    Hey guys , ive built a w/w heatpump for under floor heating . The desuperheater i have has shown to be to small and is restricting the high side , i do get alot of domestic hot water from it but it pulls COP and under floor capacity down.
    I thought i could put in a Sporlan ORI to bypass around the condenser and to maintain a certain amount of pressure in desuperheater.

    http://www.coolingequipment.co.nz/si...20bulletin.pdf

    Any one see any problems with this?

    Cheers Andy
    Last edited by AndyHX; 19-04-2018 at 07:52 PM. Reason: change cond to ds



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    75
    Posts
    11,192
    Rep Power
    60

    Re: Bypass desuper heater with Sporlan ORI

    The desuperheater is before the condenser, yes?

    So putting in an ORI/ORD bypass to bypass/backup the condenser shouldn't really affect the desuperheater flow.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Dec 2009
    Location
    New Zealand
    Age
    50
    Posts
    73
    Rep Power
    16

    Re: Bypass desuper heater with Sporlan ORI

    hi Brian , i see i made a typo above and have changed it.
    yes desuperheater is before condenser. My plan is using only the ORI not in its usual position , it will tee in before the desuperheater and join back in before condenser. i will not use ORD. This way i can direct just enough through desuperheater and majority to condenser.

    The issue i am having is desuperheater has large pressure drop and is almost doubling the kws used at 50hz that it should be using , according to coolpack and also select7.

    Thanks
    Andy

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    75
    Posts
    11,192
    Rep Power
    60

    Re: Bypass desuper heater with Sporlan ORI

    If you reduce the flow through the desuperheater are you going to get sufficient duty from it to make it worthwhile using it?

    Sorry, this isn't my area of expertise but I do enjoy reading Sporlan stuff - so - have you looked at using a 3 way heat reclaim valve?

    Have s look here .. http://sporlanonline.com/literature-...lenoid-valves/
    and read document 30-217
    Last edited by Brian_UK; 19-04-2018 at 11:05 PM.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Dec 2009
    Location
    New Zealand
    Age
    50
    Posts
    73
    Rep Power
    16

    Re: Bypass desuper heater with Sporlan ORI

    yeah those Sporlan bulletins are a good read Brian ,
    i guess the benefit of the ORI i s adjustablility , go for max desuperheat in summer cooling and back it off for winter heating.
    The 3 way heat reclaim is probably a bit supermarket sized solution and price.

  6. #6
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    75
    Posts
    11,192
    Rep Power
    60

    Re: Bypass desuper heater with Sporlan ORI

    ^^ Yep, fair comment.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  7. #7
    Join Date
    Dec 2009
    Location
    New Zealand
    Age
    50
    Posts
    73
    Rep Power
    16

    Re: Bypass desuper heater with Sporlan ORI

    Im going to give it a go , i cant see any downsides.
    I dont have a discharge service valve before the desuperheater but im quessing with the kws used condenser pressure was up to mid 60s . ill post results.
    Cheers
    Andy

  8. #8
    Join Date
    Dec 2009
    Location
    New Zealand
    Age
    50
    Posts
    73
    Rep Power
    16

    Re: Bypass desuper heater with Sporlan ORI

    Ok so got this running as good as it can , i cut in the ORi between desuperheater and condenser and i can now adjust how much flow is going through dsh , this has allowed me to increase the range i can run compressor up to.
    It was using 3kw at 40Hz , now at 55Hz it uses 2.2kw . Condensing pressure is now down from mid 60c when 100% through dsh to early 30c at full bypass.
    COP is between 6.4 at minimum to 4.9 at maximum , not including pumping .
    So pretty happy with changes.
    IMG_1663.jpg

  9. #9
    Join Date
    Dec 2009
    Location
    New Zealand
    Age
    50
    Posts
    73
    Rep Power
    16

    Re: Bypass desuper heater with Sporlan ORI

    Sorry for photo on side , if any knows how to change it ill do it.
    Thanks
    Andy

  10. #10
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    75
    Posts
    11,192
    Rep Power
    60

    Re: Bypass desuper heater with Sporlan ORI

    Thanks for the update Andy, looks promising.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  11. #11
    Join Date
    Feb 2013
    Location
    Ukraine
    Age
    41
    Posts
    17
    Rep Power
    0

    Re: Bypass desuper heater with Sporlan ORI

    Hi AndyHX

    Could you be so kind to show more pictures of your heat pump?
    I'm curious about function of ORI valve.
    Thank you.