    Refrigerate recovery



    Hearing more and more of engineers using a recovering method by using the system compressors to pump directly into the recovery bottle.
    VRV system which has two or more compressors and one requires changing or requires pressure/leak testing and using the running compressor to pump into the recovery bottle.

    Iv some safety concerns that by boing so there's no Head pressure control for the bottle if theres a possibility of over changing.
    plus what's the potential for oil loss with the working compressor moving oil straight into the bottle,with no oil sight glass on most VRV compressors.
    Is this good practice?

    plus how many of you would close the service ports/ pipe lines on a VRV and just recovery what's in the condensor to fit a new compressor. My thoughts are the compressor has failed for a reason and it's a good time to confirm the gas charge.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    75
    Posts
    11,192
    Rep Power
    60

    Re: Refrigerate recovery

    If you don't recover the whole refrigerant charge then how will you know how much to put back into the system after the repairs?

    You should always be monitoring the recovery cylinder weight so an overcharge should not happen.

    Using the push/pull method of recovery also speeds things up somewhat.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,445
    Rep Power
    37

    Re: Refrigerate recovery

    VRV's

    we would often just recover across from the condenser to the pipework by shutting the service ports. that way the whole charge doesn't need to be pulled and the amount of refrigerant moved is greatly reduced and the work gets done far quicker. You can carry on removing and PLT the condenser without worry. . Vacuum out and open the valves. Job done

  4. #4
    Join Date
    Jan 2011
    Location
    London
    Age
    38
    Posts
    43
    Rep Power
    0

    Re: Refrigerate recovery

    As brian said push/pull is how to recover its quick and easy ive got a 1/2" bottle fitting with a sight glass run the system once the liquid stops shut the system down and recover the remaining vapour i can recover 900 kgs in 4 hours uaing this method
    Never rely on shut off valves holding up may be quicker
    But its not safe pratice and what can go wrong will go wrong to many cowboys out there cutting corners to win work