Re: Calculating Reheat Capacity - For Humidity Control
Yes, this is the point. The supplied air is almost at 95%RH, as it is with all air conditioning applications. But, the set point is reached, when this air absorbers the heat inside the room as represented as a straight line (between off coil and room conditions). The issue is, I don't have enough loads, for this conditioned air to absorb heat and this causes high Relative Humidity. The specific humidity is obviously low. . . Unfortunaly, its not in design stage, the system is operational. It gives me trouble during off peak period. Summers are good. I am worried about winters and rain, when the building envelop load is also less. . .
See the attached psy chart. Don't bother the calculations, see the SHR, at part loads. scan_00032.jpg